B
barcaloco
acxtually it's 1 cable in and 1 cable out, each cable having 3 conductors., so you'd leave the existing cables as they are in the socket and piggy back a single cable into the socket., not forgetting to sleeve the cpc both ends, and if the existing cables are red/black, fix a 2 colours sticker on the CU. IR test the circuit, then once energised get a Ze and Zs reading, complete a Minor Works Certificate, job's good.
and that would only cost £50 or so? i'll get it sorted, at least i know i can crack on with the panel, cheers.
30min an hour theres not that much difference, lets settle for 45mins then tel...if you were a spring chicken lol
are you off your rocker son?