L

Lovell1991

I'm an electrician but never work on tt systems , my girlfriends parents need some work doing and asked me to help . They currently have a board In switch a 100 am rcd but no main switch to isolate the board . Does the main switch have to be enclosed in the board or can it be in its own enclosure next to the board as there is no spare ways and save them money on a new board ?Thank you
 
Hi Lovell1991 and welcome to the forum !
Do you mean that you have a 100ma 100amp rcd as the main switch in the board at the moment ?
 
a bit more detail with a photo would help.
 
No problem having an up front RCD also acting as the means of mains isolation to the CU so long as it's current rating is suitable!! The DP switch section of the RCD will have the same characteristics as a typical main switch isolator

You really need to change the existing CU to a 17th ed configuration board which at the very least gives you two sections of the CU protected by 2 X 30Ma RCD devices, and it will also be prudent to install a 100mA S type RCD up front, as an added safety measure to any UK TT system!!


Better still, get your girlfriends parents to check if a PME connection is available from the local DNO!!
 

Reply to Hi help on a tt system with the board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
832
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
653
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
329
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock