Discuss High Zs on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net
M
Maxstone89
Hi all
I have a house where all the circuits meet the Max Zs for that circuit yet the lighting circuit is testing as 747 ohms Zs
It looks like it used to be a TT system and been converted to a TN-C-S system. As its also got an main tcd before the board. Could this somehow be causing this high reading, even though the lighting circuit is connected to the main pme where all other circuits are or is their other possibilities.
Thanks max
What are the dead test continuity results for this lighting circuit? These readings will help determine why you have a high Zs.
Ran out of time, so gotta go back to sort other problems out so i am going to dead tests then, any ideas to give me a heads up.
Would be appreciated
Regards Kurtis Randle
Hi all
Thanks max
Ok mate let's start with who you are. Post #1 you're called max and post #3 you're Kurtis Randle. View Profile: Kurtis.Randle@m - Electricians Forum | Electrical Advice Forum | An electrical forum for electricians in the UK This leads me to believe you have opened a duplicate which is against forum rules. Let me know which name you want to use and I will merge the 2 accounts.
I was wondering if it had a earth. So I Google how to measure Zs without an earth, found a chat on ITE talking how...
John Peckham
"I think you can get a special meter for measuring Zs on a circuit without a CPC. I have not seen one of these meters and I do not know how they work however I have seen Zs readings on PIRs for circuits without a CPC! "
this special meter he refers to is "make it up. client only wants a satisfactory report for £50."
a R2 from CU to each point would help. easiest way is to go to each switch for starters.
Maybe cash to be made there... Just a circuit with a timer to get a random number for Zs that is under what you need.
We could stick to probs on to make it look goos and a test button to set the random figure off
Will be going back if customer will pay, but if he wont would any of you guys class this as unsatisfactory on a eicr even if there is an rcd protecting the full board?
If their was no rcd i wouldn't pass it but as there is and the result is below 1660ohms for a 30ma rcd cant remember exact figure would you pass it and add a note of recommendation?
If you have 747Ω as the resistance of a domestic circuit then there is something very wrong, this is equivalent to a 60W light bulb connected through the cpc.
Even though it does meet the 1667Ω requirement for a 30mA RCD it is very likely that you have a very poor / corroded connection somewhere (or a major wiring error) and that this will get worse over time.
There is no sensible way this can be a result from a satisfactory circuit.
The fault needs to be identified and resolved.
However if the customer does not want to do it then you do have to leave it, but I would recommend putting an advisory of a faulty circuit in writing.
I would guess.the problem is, did you measure some thing wrong and it looking daft on you
Maybe do.it for free to make sure you didn't cook up
If you did cook up some way it would look like your trying to con the person
Whats with the sarcastic remarks.
Please do not comment if its gonna be sarcasm.
I think Duane was just thinking out aloud there and was not trying to be sarcy... He was just saying are you 100% that the test result is the correct one given all others are OK. We all makes mistakes from time to time after all. I can see Duane's point that if it was a mistake then it could look like you were creating work.
Reply to High Zs on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...