Fair enough, just the amount of people being sarcy on here is just daft, so if you weren't then no worries.

Yes all the readings on both light citcuits where all coming out at the same which is odd.
 
  • Like
Reactions: 1 person
So, there is TWO Circuits, two MCBs 6A about, and all the Light Points the Zs is 747Ohms when you need Zs Max of 7Ohms (5A) and 5.87Ohms (6A) I think [NB i put i think, as someone may correct me]
So 747Ohms is not great even if it was 7.47Ohms still above the Max Zs

As Zs = Ze + R1 + R2 , if R1+R2 is Dam high you know the fault is on it, which would be the logical thing
But any thing could happen i guess, could be lose wires hangin in a pool of water, or just hold on by one strand.

Sounds a bit like someone has wiring a Light bulb in series, Live to Bulb to Light Sockets, then as long as one light comes on you wil get the light on, but would give you a high ohms reading.



I know your with NICEIC (looked up on your other account
NICEIC Consulting
Tel: 0500 600 545
Email: [email protected] - See more at:

Im not one who can be
sarcasm because of my problems, it will just blow back at me.
I can be dam Strange like the Uniform YCMA Post, and As you Noticed the Zs Test without a CPC, what you know is impossible but people still get figures for, so i googled it and someone JOKED about a Meter that could measure it.
But as your results, I understand wanting to get every thing perfect and when things aint spot on, one can tend to get worried. I do JOKE to Try and Lighting the mood, im like that in Group Orgies too, ----ing a Coin heads of tails for what end one gets.
 
Last edited by a moderator:
What job are you doing here?
Are you working on the lighting circuit or are you carrying out periodic testing?
 
So if customer doesnt want a return visit, do i code it c2 on eicr or as it has an rcd or c3?

U would say c3 as if it was a tt system it would pass??

And As its already there, if a new circuit then it would be a no no.??

What would you guys code it?

Thanks
 
Last edited by a moderator:
So if customer doesnt want a return visit, do i code it c3 as it has an rcd or c2?

U would say c3 as if it was a tt system it would pass??

And As its already there, if a new circuit then it would be a no no.??

What would you guys code it?

Thanks

What do you mean by a return visit? What exactly is the job you are doing here?
 
Carrying out an Eicr.

I have possible ideas why which some have been stated, just thought why not ask in case a simpler answer/possible cause is out there
 
So if customer doesnt want a return visit, do i code it c3 as it has an rcd or c2?

U would say c3 as if it was a tt system it would pass??

And As its already there, if a new circuit then it would be a no no.??

What would you guys code it?

Thanks

I'm assuming that you are undertaking a PIR here,

Whether the customer wants a return visit or not is not the point, you've carried out an inspection so you must code as you see fit.
Also you can't code as you would a different system, the earthing system you have is what you must assess the installation on.

For what it's worth, providing I've understood correctly I would give this a code 2.
 
Carrying out an Eicr.

I have possible ideas why which some have been stated, just thought why not ask in case a simpler answer/possible cause is out there

Right, it's an EICR so you are there to carry out the tests, record the results and make your decisions about coding, you would not normally be there to do any investigation of the faults.

You have a Zs result which is abnormally high considering the supply type (TNCS) so there is a very strong possibilty that there is a fault there and it's not just a circuit with a high Zs. So I would be inclined towards a C2
 
  • Like
Reactions: 1 person
Would anyone else code it C1/C3??

I think C2 seems correct, just always worth asking other people's opinions and thoughts how they have come to it.
 
it's a C2 in my book. ( an exposed part could become live under fault conditions. with no cpc, then this could be lethal.) with a comment that further investigation is required.
 
Would anyone else code it C1/C3??

I think C2 seems correct, just always worth asking other people's opinions and thoughts how they have come to it.

What do you, as the qualified experienced person, think it should be coded?
 
As said i think c2 but was seeing if the rcd made any difference to the code required.
 
not in my book. with a reading of 700 odd ohms, that could easily become >1667 ohms and so negate the use of the RCD as fault protection. C2 all day.
 
  • Like
Reactions: 2 people
I would be putting a C2.

If it had been a TT then perhaps a C3 if it had a thick, deep, stable earth rod or perhaps mulitiple earth rods. But if your other Zs figures meet the required figures and this 'one' doesn't then I guess the earthing arrangement must be as you have stated (PME), so I would say a C2.

I find it strange when I put down a C2, or perhaps multiple C2's and the customer doesn't get back to you! This has happened twice and I know for certain that on one occassion they have not had the work carried out.
 
I think when i did my 2330 Level 3 and the EAL 2395 they both gave me this Document as as kind of ref guide

http://www.----------------------------/mediafile/100404922/Best-Practice-Guide-4-Issue-4.pdf
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High Zs on lighting circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
Maxstone89,
Last reply from
DuaneMHunt1976,
Replies
34
Views
12,107

Advert