So, there is TWO Circuits, two MCBs 6A about, and all the Light Points the Zs is 747Ohms when you need Zs Max of 7Ohms (5A) and 5.87Ohms (6A) I think [NB i put i think, as someone may correct me]
So 747Ohms is not great even if it was 7.47Ohms still above the Max Zs
As Zs = Ze + R1 + R2 , if R1+R2 is Dam high you know the fault is on it, which would be the logical thing
But any thing could happen i guess, could be lose wires hangin in a pool of water, or just hold on by one strand.
Sounds a bit like someone has wiring a Light bulb in series, Live to Bulb to Light Sockets, then as long as one light comes on you wil get the light on, but would give you a high ohms reading.