Discuss Honeywell wireless stat DT92E in the Central Heating Systems area at ElectriciansForums.net
hi guys, customer has no thermostat for his heating so he brought a Honeywell dt92e. I am trying to install it but can't link it up with the programmer (2 channel Drayton) I have wired the stat up with a perminant live and it fires the boiler. But I can't get it to work properly with a programmer as well. there isnt a wiring diagram containing a programmer, any ideas.
Is there two x two port valves or 1 x three port valve?
2 two port, one for hot water one for heating
Okay the relay box needs permanent live and neutral to terminals L & N then CH ON from programmer connects to terminal A and brown from CH valve connects to terminal B.
If there is no thermostat originaly then CH ON from programmer and brown from CH valve will be connected together in the same terminal in the wiring centre. Just separate them and connect CH ON to A and brown from valve to B along with permanent live and neutral to terminal L & N.
Reply to Honeywell wireless stat DT92E in the Central Heating Systems area at ElectriciansForums.net
Hi there, We have recently replaced our central heating programmer with a Honeywell ST9400C. We now want to replace our old wireless room...
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
It has become a common occurrence that my boiler is failing to respond when the thermostat kicks in. I hear an audible click from the heatlink...