electric will
Sparkykus. Your brave, I considered taking tncs the blood tub I'm doing seems to me mainly made of wood and plastic.
Who's Buff ?
;-)
rcd can be at the mains or local to hot hub if using swa , either is ok.
yes , connect swa and earth conductor together at the CU.
Unless there's a specific reason, why can't you export it?
There are specific circumstances where you cannot use Tncs (like caravan parks I believe, it has to be rodded, as a fellow forum member I know who works alot for the Caravan Club will testify).
Is a hot tub one of these instances?
The only other problem is with services like water pipes - which means main bonds also need to be extended- which could be a pain.
agreed , so in that instance you have a choice of running a 10mm earth bond from the MET to the outside pipes or , bang in earth rod near hot tub.
most choose the earth rod method if its a long run back inside and they're only using a 6mm cable anyway.
Apart from that I 'd rather have a Zs of 0.3 than 37 or 17 or 7 .....?
so would i lol