devonsparky

This is a follow up to a thread I started yesterday.

I have been working all day installing a hot tub situated outside on a patio slabbed deck.

Contrary to what I was told, it was TN-C-S supply so here is how I have wired it.

  • From Henly blocks - 25mm tails to a one way board (Main Sw RCCB - 50A MCB)


  • 10mm 3 core SWA from board to 63A rotary isolator and from rotary isolator to hot tub


  • Earth rod with 10mm G/Y back to one way board and then used one core as an earth to the hot tub and connected the armour to the earth bar too.



Time beat me today so I have not connected into the Henly blocks yet and tested .......................... Is this how you guys would have done it. 10 years in the game and an approved electrician and it's still nice to get feedback off of this forum !! ha ha
 
There are specific circumstances where you cannot use Tncs (like caravan parks I believe, it has to be rodded, as a fellow forum member I know who works alot for the Caravan Club will testify).


Is a hot tub one of these instances?

The only other problem is with services like water pipes - which means main bonds also need to be extended- which could be a pain.


Apart from that I 'd rather have a Zs of 0.3 than 37 or 17 or 7 .....?
 
Unless there's a specific reason, why can't you export it?

The Dno's dont approve of extending their PME earth beyond the equipotential zone of the building in which the supply is located.
This is only an issue if there is exposed / extraneous metalwork at or around the hot tub ,
as in the unlikely event of a neutral break this metalwork may rise to a dangerous potential.
hope this helps.
 
I replied in the other thread, I installed my tub using the supplied tncs earthing arrangement also putting a rod in at the tub end. This rod was well below 22 ohms as stated in the regs, the only problem I had was when you got out the tub and one leg was on the floor and one in the water you could feel a shocking feeling, slight difference between true earth and suppliers earth, therefor I disconnected the suppliers earthing and made the tub tt. Alls fine now so that's how I install them from now on!
 
There are specific circumstances where you cannot use Tncs (like caravan parks I believe, it has to be rodded, as a fellow forum member I know who works alot for the Caravan Club will testify).


Is a hot tub one of these instances?

The only other problem is with services like water pipes - which means main bonds also need to be extended- which could be a pain.
agreed , so in that instance you have a choice of running a 10mm earth bond from the MET to the outside pipes or , bang in earth rod near hot tub.
most choose the earth rod method if its a long run back inside and they're only using a 6mm cable anyway.



Apart from that I 'd rather have a Zs of 0.3 than 37 or 17 or 7 .....?
so would i lol

.......................
 
But if you export and have rcd protection how can people feel the tingle when getting in and out. This must be potential difference with the value at the met(via tncs) and the ground where the tub is located, part of body in the water and foot on the ground. Surely the max difference would be 50v any more the rcd would trip
 
last hot tub i did was off TNS , didnt bother with any rods :-D

If the hot tub was located on bare ground or grass, i think i'd be also installing a rod, even if it was a TN-S supplied installation. Your still going to get a potential difference between true earth and the DNO TN-S earth.....

As for the Regs, i think they state somewhere, that a TNC-S supply can be used, for supplying hot-tubs and the like provided an earth electrode of a certain value is also provided.... I think that value was around 20 ohms, but i wouldn't swear to it...
 

Reply to Hot tub installation ! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top