Hi, if I have a DB that has a main switch and then a seperate 63A RCD that protects number of single circuits . how do i include that RCD in the schedule of test results?
and should i include its test results for each circuit test results ?

Many thanks
 
Just put the RCD on its own line with all the applicable details filled in.
I usually copy the RCD times to each of the circuits that the RCD protects. I know some on here do not do this, but as long as it's clear that each circuit has RCD protection that's what matters.
 
That’s how I do it.
 
just put down rcd protected circuits on the line before the circuit 1 or 2 or 3.
 