hyrdoboil trips mcb? Element is 2.4kw ohms test was 23 Ohms and IR was 300 odd. Had disconnected element from thermostat and power did not trip but element seemed perfect
 
Hi,what else is on the same circuit,and 300 odd what?

Sometimes,it takes a few cycles or change of duration,to tempt a faulty element.
 
Hi,what else is on the same circuit,and 300 odd what?

Sometimes,it takes a few cycles or change of duration,to tempt a faulty element.
That seems to be all on circuit. IR was 300Mohms when the customer had turned the water boiler on it tripped mcb straight away
 
Have you seen it trip? If it's repeatable try a toaster in that outlet and see what happens. If it trips too then perhaps N-E cable fault somewhere.
 
Have you seen it trip? If it's repeatable try a toaster in that outlet and see what happens. If it trips too then perhaps N-E cable fault somewhere.
The O.P. is saying MCB N-E fault doesn't usually trip a MCB unless incorrect info.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
SCOTLAND

Thread Information

Title
Hydroboil trips mcb ???????????????????????????
Prefix
N/A
Forum
Electrical Appliances & Whitegoods Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Greengo1990,
Last reply from
Wilko,
Replies
8
Views
1,886

Advert

Back
Top