If the main argument here is that external factors can cause a ring to split which can cause 32a protection to be too much for the cable .....what about if an external factor causes the 20a radial to be redirected / modified to travel through an insulated stud wall ref 103 or 101? My point being external influences can happen at any point and change characteristics.
 
Anyone uses 25A instead 32A for rings ?

I did, once, on a recent board change. Early 1980s bungalow with all cables in loft, later covered with insulation. Ref meth 101 not allowed.

According to my copy of the IEE wiring regs 14th edition amended 1976, reg A.33 (ii) "for ring final sub-circuits, the current rating of the conductors forming the ring is not less than 0.67 times the rating of the fuse or circuit breaker protecting the final sub-circuit". Putting it on a 25A would have it comply with the regs back then.

It wouldn't comply with current regs, but my 3rd party guy notifying it was happy with it (I'm not yet on a scheme), and it was a lot less itchy than putting conduit on every damn cable up there.
 
@Pretty Mouth If it happens and found an existing circuit on twin 4mm cable radial circuit i install 25A and remove the 32A.
I also install 25A on some circuits for example if is a 1 bedroom area only, or a living room area etc which i know there only few sockets and to use 30A load seems not possible.
On areas like the kitchen or machinery areas like garage i use 32A
 
I did, once, on a recent board change. Early 1980s bungalow with all cables in loft, later covered with insulation. Ref meth 101 not allowed.

According to my copy of the IEE wiring regs 14th edition amended 1976, reg A.33 (ii) "for ring final sub-circuits, the current rating of the conductors forming the ring is not less than 0.67 times the rating of the fuse or circuit breaker protecting the final sub-circuit". Putting it on a 25A would have it comply with the regs back then.

It wouldn't comply with current regs, but my 3rd party guy notifying it was happy with it (I'm not yet on a scheme), and it was a lot less itchy than putting conduit on every damn cable up there.
14th edition bit behind the times Mate, it's the 18th now nearly
 
I'm surprised what this is still going.
I'm feeling left out so I would just like to say, this should have finished at @wirepuller post #20, which pretty much sums this thread up.
 

Reply to I never install ring circuits, the potential for danger is unacceptable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon all, A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD...
Replies
24
Views
4K
Hi all. Long time lurker, first time poster. I am not an electrician but I enjoy learning as much as I can. I am currently renovating a house...
Replies
10
Views
1K
The Ghost
T
S
Greetings all, I'm looking for a bit of advice. I'm not actually an electrician, but I am an electrical design engineer and I am aware of the...
Replies
33
Views
3K
Hi guys, I have come across two problems today well acutely three so I will list them first.. 1st Testing a 4mm radial circuit today or so I...
Replies
18
Views
7K
Engineer54
E
D
Be honest here guys...When you do your testing, do you do it exactly the same as you would during a college assessment on every installation you...
Replies
59
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock