There was a change with the 18th. 16A site sockets are now required to be switched and interlocked, so any unswitched are now C3 on an EICR.
That’s only in specifically mentioned uses though, like caravan parks etc. I think the general concept of ‘industrial’ outlets in a domestic situation just hasn’t occurred to anyone?
 
From my earlier example, a 13A plug to a 16A socket (no shutters) for a caravan as an example…. Ok, the holes are bigger… but could be the same argument for the “figure 8” leads for radios and tvs… in fact, IEC leads for computers as well.

Once plugged in, it is possible to stick a metallic object into the socket end holes.



A bit off - direction to the original question…. In which case a 16A interlocked socket on a dedicated 16A radial. Not on the rfc with regular 13A
 
That’s only in specifically mentioned uses though, like caravan parks etc. I think the general concept of ‘industrial’ outlets in a domestic situation just hasn’t occurred to anyone?
Absolutely!

The problem is that when regulations are written, they tend to start from a "common sense" thinking.

Unfortunately people just try to find technical ways around them; interpreting them in a way that allows themselves to implement something that realistically ought not be done "the regs say red isn't acceptable, so it's OK to use cherry as it isn't technically red"

As such the regs end up chasing what has been done rather than catching it before it happens.

Three sayings come to mind:

Making things foolproof is impossible as fools can be very inventive.

Common sense, is neither common, nor sensible.

Yosemite Park ranger:
The problem with designing suitable waste bins, is there is considerable overlap between the average bear, and the stupidest human visitor
 
The problem is that when regulations are written, they tend to start from a "common sense" thinking
Absolutely, and I think it can work both ways. Some people find every possible way to reinterpret the regs to try and avoid something they don't want to particularly do for what ever reason. On the other hand, some people interpret the regs in a way that everything is black and white and that anything slightly askew is deemed unacceptable.
Then you have those (the ones with common sense) that use the regs for their intended purpose in that they are a guide to the minimum requirements deemed necessary to ensure installations are done to a common safe standard. There will be on occasion however, where some thought into the intended application/use of the install needs to be considered and what potential risks could be factors. The regs though, no matter how profound and detailed will not be able to cover all circumstances, this is where the installer needs to use their noggin and apply some sense.
 
Has nobody thought to fit the unshuttered socket in an enclosure which can only be opened with a key and ensure that anyone with access to the key is correctly trained?
 
Has nobody thought to fit the unshuttered socket in an enclosure which can only be opened with a key and ensure that anyone with access to the key is correctly trained?

Why? Putting the socket inside a locked enclosure defeats the point if. A socket doesn't it? It might as well be a hard wired connection at that point.
 

Reply to I want a 16 amp socket in the garage with 3 double sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
717
Is this ok? 32amp breaker with a 6mm wire leading to fused cooker switch. This then leads with 6mm cable to hardwire point. Can i hardwire 2 x...
Replies
11
Views
732
OLDBOY
O
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Good morning, Ive a dry covered area by the side of the house where I’m wanting to some welding art, I bought a 200 amp tig welder , that says it...
Replies
3
Views
803
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
268

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock