0
I am adding a socket to an existing ring circuit in a 3 phase cu
All the connections have to be done at the cu as the sockets are inaccessible
I am basically extending the ring circuit
How do I identify the correct ring legs (L,N) (L,N) as they are not taped and the trunkin is packed with cables?
 
Connect L+N of 1 leg and L+N of the other leg at the DB and then test resistance between L+N at every point around the ring

If you have connected the 2 separate legs correctly then the resistance at every point should be the same with the exception of spurs which will be slightly higher

If you have connected incorrectly then the resistance will increase at every point until you reach the centre of the ring and then reduce as you move away from the centre back to the DB
 
Connect L+N of 1 leg and L+N of the other leg at the DB and then test resistance between L+N at every point around the ring

If you have connected the 2 separate legs correctly then the resistance at every point should be the same with the exception of spurs which will be slightly higher

If you have connected incorrectly then the resistance will increase at every point until you reach the centre of the ring and then reduce as you move away from the centre back to the DB
How does that help identifying the conductors within the trunking.
 
How does that help identifying the conductors within the trunking.
OP asked how to identify legs in the DB...
All the connections have to be done at the cu as the sockets are inaccessible
How do I identify the correct ring legs (L,N) (L,N)
And I gave the solution
If OP asked how to identify which leg is which in trunking then I would have suggested using a toner
 
Connect L+N of 1 leg and L+N of the other leg at the DB and then test resistance between L+N at every point around the ring

If you have connected the 2 separate legs correctly then the resistance at every point should be the same with the exception of spurs which will be slightly higher

If you have connected incorrectly then the resistance will increase at every point until you reach the centre of the ring and then reduce as you move away from the centre back to the DB
I was thinking of going to what I think is the first socket in the circuit and disconnecting it,touch both lives to earth then go back to the board and measure each live to earth finding the smallest residence and do the same for the neutrals to find the first leg into the socket
Would this method be ok ?
 
I was thinking of going to what I think is the first socket in the circuit and disconnecting it,touch both lives to earth then go back to the board and measure each live to earth finding the smallest residence and do the same for the neutrals to find the first leg into the socket
Would this method be ok ?
This might work or not depending on how it was wired as you probably have no idea where the 2nd leg is going and could be going a similar distance to the 1st leg so this method is not reliable which is why rings are tested the way they are (interconnect at db and test at every point)

I suggest doing your ring dead tests before (to confirm which leg is which) and again once work has finished as normal
 
This might work or not depending on how it was wired as you probably have no idea where the 2nd leg is going and could be going a similar distance to the 1st leg so this method is not reliable which is why rings are tested the way they are (interconnect at db and test at every point)

I suggest doing your ring dead tests before (to confirm which leg is which) and again once work has finished as normal
It has been suggested to not add the socket to the ring but to add a spur from the mcb this would mean 3 lives and 3 neural wires at each mcb terminals
Is this ok to do so because it would life alot easier?
 
What brand is the rcbo. If it is Memshield 2 or Proteus you may struggle with a third line conductor. Just spur from an existing socket.
 

Reply to Identify ring circuit legs that are wired in singles in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
242
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock