the manufacturer has done the diversity calculation for tou and 3.68kw is about right

If they have done this calculation for you they would need to stipulate that it is for 'normal' domestic use and presumably assume you have a socket outlet on your cooker switch?
Bear in mind the calculation of diversity allowance is the responsibility of the installer - not the manufacturer.

You could be installing this hob in a commercial kitchen.
 
lol just take it on the chin mate its just part of this forum , doesnt matter what you ask you will get all sorts of ---- off people , just go with it

Sorry matey, can't agree with that. Just need to think about what you post, the more constructive the OP, then the more constructive the replies will be.
 
lol just take it on the chin mate its just part of this forum , doesnt matter what you ask you will get all sorts of ---- off people , just go with it

Sorry matey, can't agree with that. Just need to think about what you post, the more constructive the OP, then the more constructive the replies will be.
and the problem with my OP is what exactly?
 
Agree with Murdoch. There are a hell of a lot of good posts with sound advice given. Daz
 
and the problem with my OP is what exactly?

Without wanting to put words into Murdoch's mouth, I think he is replying to iamelectric's comment about it not mattering what you ask you will get ---- back. Daz
 
Without wanting to put words into Murdoch's mouth, I think he is replying to iamelectric's comment about it not mattering what you ask you will get ---- back. Daz

Spot on DPG. Look at IAMELECTRIC's posts and you will see precisely what I mean.
 
For anyone interested went back to this job a week or so ago. Kitchen fitter had taken my outlet plate off and instead installed a single socket outlet as the hob came with plug top. The customer had decided to change the hob that they were having as the previous one couldnt be guaranteed before xmas. Its a little ott but they now have a 45a cooker switch controlling a single socket outlet wired in 6mm2
 
For anyone interested went back to this job a week or so ago. Kitchen fitter had taken my outlet plate off and instead installed a single socket outlet as the hob came with plug top. The customer had decided to change the hob that they were having as the previous one couldnt be guaranteed before xmas. Its a little ott but they now have a 45a cooker switch controlling a single socket outlet wired in 6mm2




Nothing wrong with that
 
For anyone interested went back to this job a week or so ago. Kitchen fitter had taken my outlet plate off and instead installed a single socket outlet as the hob came with plug top. The customer had decided to change the hob that they were having as the previous one couldnt be guaranteed before xmas. Its a little ott but they now have a 45a cooker switch controlling a single socket outlet wired in 6mm2




Nothing wrong with that
i know, like you said not having the full information and being unable to read minds i was always going to err on the side of caution as stated in earlier posts. Obviously had i the information to begin with i wouldnt have designed it in such a fashion.
 
Kitchens are usually the number one room for changes, wire it once and no doubt they'll swap the gas hob for a ceramic, add under unit lights, move the sink, drop the ceiling, move the whole kitchen a foot to the right and sack off the fan oven for an aga.....

I hate kitchens! Haha :lol:
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

leep82

Arms
~
Joined
Location
Stoke on Trent
Business Name
L.M.P Electrical

Thread Information

Title
induction hob cable size
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
leep82,
Last reply from
Thefailsafe2012,
Replies
33
Views
10,548

Advert