I've asked questions around the machines but nothing obvious or sensible from the operators that imply they are doing anything out of the ordinary. I see no logical reason but two machines not working.. Got to be something quite simple either machines or a fault. Not sure if a N fault on the supply side would manifest itself like this given the issue is consistent across phases; I've try and get down to check Ze & Zs but if it's a fault I can't see why it can be anything other than DNO side.Makes no sense, frankly. You're seeing a volt drop on start-up that's still 8v HIGHER than nominal. Also - do the maths - you're losing 10v at only a maximum of 16A?? That's a massive resistance. Also, you've not said anything about circuit overload protection kicking in which suggests that the issue isn't current.
Without wishing to sound condescending, are you sure the machines don't have some sort of transport locking pin still in place that's simply not allowing them to spin?