D

Davey1988

Hey guys

I want help on this forum about cpc and I heard I won't get any am I right?
 
Last edited by a moderator:
Calculate cpc size using the adiabatic equation, exactly the same as any other circuit.

And put your best tin hat on before anyone else answers this, if you aren't on a wind up you are going to be catching some serious flak!
 
No ze provided and unable to measure. Not sure on the cable sizes yet especially cpc So ain't worked out r1 and r2.

Lovely.
 
To save future embarrasment I deleted it.

2 phases. No neutral. And cpc
80 amp fuses per phase. Max leakage imo can be no higher than 160amp.

First time in dealing with welders not 100%
 
No, they use the cpc as a cpc and a neutral as a neutral if one is required. It sounds like the machine you have is designed to operate on two phases of a three phase supply, unless of course it's designed for a two phase supply?

You need a lot more than a little guidance, you clearly don't understand the first thing about the job you are attempting to do.
 
thinking worst case senario. Do welders use a cpc to act as a neutral. little guidance is all I need and I'm finding it really hard to get it on here.

Some welders have 200amp - 400amp earth clips.....

I think you are getting confused with the terminology,referring to the OUTPUT side of the machine.

The terms and figures only make sense,if this is the case.

Do a bit of research,and all will become apparent...but do not attempt,if unsure,and some other human is to test its' operation...:conehead:
 
Think along the lines of electrode (live) and work piece (neutral return). The I/P and O/P are two separate entities.

Where I’ve seen things go badly wrong is when the CPC has been used for the return. Do some reading on the subject, as a hint, don’t bother looking in BS7671.
 
Think along the lines of electrode (live) and work piece (neutral return). The I/P and O/P are two separate entities.

Where I’ve seen things go badly wrong is when the CPC has been used for the return. Do some reading on the subject, as a hint, don’t bother looking in BS7671.

Yep, I recently had a call out because a welder had set the cpc on fire in the DB and it even made the trunking rattle, lol. I repaired the circuit and offered to check the welder to make sure it was wired correctly but they thought it was dangerous so the had ditched it before I got there...
 