Cheers, Pete That's how I'm doing it at the moment, but there are times when all I can give are, R1+R2, Zs and insulation info. It's just a bit frustrating :-(
Just do the dead tests, tell your client you can't issue an installation cert until he gives you a down time slot, unless one of his maint guys is told to work live he can't use the new install, see how long that takes, invoice him for the install only and say you will certify when he agrees a down time slot, difficult I know but I used to do it with high end Civil Servants, I know I was paid regardless but it did work when they couldn't do the things they wanted to do to keep the country running, or so they thought, nothing worse than a self important Dennison from the corridors of power,
LIMITATIONS!
As long as you can justify limitations on your EIC then state that shutting down for correct testing of Ze etc is not viable. If there is an up to date EICR available then you could use those readings and give the above reason for doing so.
It would depend on scope of the work you are carrying out as well, a major job would not justify limitations, but a new radial circuit from a sub-DB for example hardly justifies major disruption and cost implications when perhaps a Zdb reading with no shutdown is perfectly adequate.
I was running a new circuit from a board. Simple double socket. I tested insulation, R1+R2 before hooking up, and Loop impedance from the socket once it was live. But I couldn't check Ze or lpf as the board was live and the other circuits were in use. I did inform the client and marked the lim's on the certificate. Thanks for all your help :-)
Commercial premises that have had a forward thinking electrician in during a shut down usually have the useful addition of Ze and Ipf written on the incoming chamber/panel board in black marker.
Always nice to find that.
Installation certificate, but can't shut down.
Duncan Bennett,
davesparks,