LIMITATIONS!
As long as you can justify limitations on your EIC then state that shutting down for correct testing of Ze etc is not viable. If there is an up to date EICR available then you could use those readings and give the above reason for doing so.
It would depend on scope of the work you are carrying out as well, a major job would not justify limitations, but a new radial circuit from a sub-DB for example hardly justifies major disruption and cost implications when perhaps a Zdb reading with no shutdown is perfectly adequate.
I disagree Ze is a required test and there should be no Limitations as there is no provision on an EIC to introduce Limitations.
 
Commercial premises that have had a forward thinking electrician in during a shut down usually have the useful addition of Ze and Ipf written on the incoming chamber/panel board in black marker.

You should see this place, Andy. It's been running for decades and they have not ONE certificate.

Substitute Ze for Zdb and note on the cert. As for Ipf why could you not do that?

Sintra: Yes, I can do that. I'm just being pedantic; Ze is external and you can't do that without disconnecting the main earth. And, yes, you're right about LPF. My bad!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Installation certificate, but can't shut down.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Duncan Bennett,
Last reply from
davesparks,
Replies
20
Views
2,520

Advert

Back
Top