Chap, there is a good reason why the biggest domestic instant water heater is rated at about 15kW, that is because it will draw some 65.22A from a single phase supply and depending on how the cable is installed (insulation, buried in walls etc) and what cable is used it would not only look damned ugly, but would be something in the region of 16mm² or possibly 25mm² SWA! To work this out accurately would need to know actual circuit specs, but do you start to understand?
If you bought the 24kW unit on your list that will draw some 104A from the supply which would be either a 25mm² or a 35mm² SWA...wholly impractical.