Instrument for Testing a Lightning Conductor

S

slingshot2000

Is it possible to test Lightning Conductor with an Earth Loop Impedance Tester ?

Discuss . . . . . . . . .. .
 
It's nice to post something and not have it deleted because it is a question regarding the new site sponsor !

Take that as you like .

Any views on lightning conductor testing will be greatly appreciated.
 
I would say very much so! But you'd have to know what was required from the testing procedure....
 
Surely an earth resistance tester (the one with the long wires and the T spikes) would be better unless the area around the rod(s) is built up or paved.
 
Test method 2. The wondering lead
I think one on the top of the rode and one at the incoming earth
This will give R and guess adding it to Ze.will give you a path to a transformer and low as possible like a Tt system

http://m.youtube.com/watch?v=i3qSYAW5Jcw
 
Last edited by a moderator:
Surely an earth resistance tester (the one with the long wires and the T spikes) would be better unless the area around the rod(s) is built up or paved.

This particular installation is a Church surrounded by a tarmacked car park.
Also, to prevent theft of he copper rod, the electrode is contained in a steel tube to a height of approximately 4M.
 
I have only had small involvement in lightning protection, but when I have the requirement was <10ohms to earth from any point on the installation/ <10 ohms from the highest point to earth.
Not an electrode resistance of <10 ohms to earth.
 
I have only had small involvement in lightning protection, but when I have the requirement was <10ohms to earth from any point on the installation/ <10 ohms from the highest point to earth.
Not an electrode resistance of <10 ohms to earth.
That I why I asked for a discussion, there is so much conflicting information out there. I am currently trying to working my way through Megger's "Down to Earth", and thought a discussion may help.
I mentioned to an old hand what I was looking at and he told me remembered doing this with a loop tester.
 
would have thought insurance company would want certification from lightning protection company
 
If the building has a single lightning conductor the maximum reading of the rod should be below 10 ohms. We normally do a fall of potential test on a single earth if possible otherwise test off a "known earth" such as a street light or the earth on a plug socket in the building.

Should really be done by a lightning protection company though.

Megger DET3TC is what we use.
 
Last edited:
That I why I asked for a discussion, there is so much conflicting information out there. I am currently trying to working my way through Megger's "Down to Earth", and thought a discussion may help.
I mentioned to an old hand what I was looking at and he told me remembered doing this with a loop tester.

You need to get a copy of the BS for lightning protection and test in accordance with that, not free help guides.
 