in a cafe at present working and is a load of stainless steel in one corner for washing up etc..

i want to do a test to see if needs bonding

im nearly certain i I r test from earth isco to stainless steel in question and test @ 500vdc and if under 22k ohms it should be bonded,

is this info in big green book(bs7671) all electrical equipment in this area is ip44 rated.. any guidance welcome
 
What makes you think the stainless steel is an extraneous conductive part? Is it bolted into the ground or in some other way significantly "earthy"?
You are correct about testing though, test from earth MET (remove all parallel paths) using IR tester at 500 volts, if the result is less than 22k ohms then bond it!
 
so turn of main supply, remove earthing conductor and test accordingly, all im doing is new lighting and like for like fittings and noting anything that doesnt look right. i.e ring ciruit on 40A breaker
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

i=p/u

Arms
-
Joined
Location
Northern Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
insulation resistance testing stanless steel
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
i=p/u,
Last reply from
i=p/u,
Replies
9
Views
1,671

Advert

Back
Top