Discuss insulation resistance testing stanless steel in the UK Electrical Forum area at ElectriciansForums.net
i=p/u
in a cafe at present working and is a load of stainless steel in one corner for washing up etc..
i want to do a test to see if needs bonding
im nearly certain i I r test from earth isco to stainless steel in question and test @ 500vdc and if under 22k ohms it should be bonded,
is this info in big green book(bs7671) all electrical equipment in this area is ip44 rated.. any guidance welcome
What makes you think the stainless steel is an extraneous conductive part? Is it bolted into the ground or in some other way significantly "earthy"?
You are correct about testing though, test from earth MET (remove all parallel paths) using IR tester at 500 volts, if the result is less than 22k ohms then bond it!
so turn of main supply, remove earthing conductor and test accordingly, all im doing is new lighting and like for like fittings and noting anything that doesnt look right. i.e ring ciruit on 40A breaker
Reply to insulation resistance testing stanless steel in the UK Electrical Forum area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Greetings! Newbie here! We have 3 phase installation in our Lighting dimmer rack. During Insulation Resistance testing on Earth-Nuetral, readings...
5K
On initial verification of new installations I have been having a hard time with insulation resistance. With RCBOs, fixed LED luminaires...
