Ok so I have been to a domestic property today, and carried out an EICR, couple of issues flagged up with regards to the usual no RCD protection bonding cables etc now its quite a big property and the customer has gone with my advice of RCBOs but one question. Most circuits tested fine but the kitchen ring has an IR reading of 3.4 mega ohms.... my question is as this is within the limits (greater than 1) is this ok to still upgrade and issue an EIC I have had a quick look behind all the sockets to check for anything obvious but nothing now i would usually recommend this is investigated further as a side note but the kitchen isn't the easiest place to do this and with an IR reading of 3.4 it is deemed ok and therefore no classification code is required just something I wonder if anyone else has come across before

Thanks
 
Well it is a pass even if on the rather low side. Still with RCD protection it is a lot safer no matter what!

Was it tested with everything unplugged, or done by L+N to E as some things like washing machines too hard to move out to access sockets?
 
As above! Probably a dirty or damp back-box causing it, though worst-case some fitter has nicked the cable with a screw or nail.

At my own house I found one of these when I replaced the kitchen bench top last year. The back rail on the wall had a screw in contact with the L of the RFC The cable was correctly in a zone and otherwise worked fine. But IR was about 10 meg if I recall correctly.
3ACBC895-CF9C-496C-B237-D222C7AC3E7A.jpeg
 
If both L to E and N to E are similar and in the few meg region then I would guess damp/dirt. If N to E+MET is high but L to E+MET is low I would worry about cable damage by a screw or similar.
 
At my own house I found one of these when I replaced the kitchen bench top last year. The back rail on the wall had a screw in contact with the L of the RFC The cable was correctly in a zone and otherwise worked fine. But IR was about 10 meg if I recall correctly. View attachment 61247

Looks like the cable route is even marked on the wall !
 
That is assuming the kitchen fitter could read English, I had a Polish worker on one of my sites that ripped up a piece of plywood that was shot fired to the concrete floor, it had big red lettering on it saying "Hole Under" he jemmied it up and walked forward and fell six stories down a service shaft, at the bottom was all the polystyrene that had been used to form the holes, the shaft was too small for him to turn during the fall and he just sustained a broken leg and hip, he was very lucky, but the accident report was interesting to fill out.

My most interesting accident report concluded "Too many knobs and not enough Knots"
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
IR reading of 3.4 mega ohms, upgrading CU help
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29
Unsolved
--

Advert

Thread statistics

Created
NellyManjaro,
Last reply from
DefyG,
Replies
29
Views
3,167

Advert

Back
Top