I know this may seem like a stupid question, but here goes.

Example...

You have an existing RFC and spur off to a SFCU to feed a flood light for example.

Connect it up, do R1+R2, Zs etc,

but IR, I disconnect N and then run 250v as a start between L-N, then L-E, then N-E, then if all clear (acceptable reading say >100M), I do it at 500v and take the risk.

But first I go round the entire flaming house unplugging everything as there's no telling whats on what circuit, if its SP or DP sockets and just switching off may not be safe, or have missed something.

I know I can do it LN-E @ 500v, but am I missing a trick here?

My issue is, I get a lot of customers wondering why I am essentially interfering with the the rest of the house (unplugging stuff) just because I have fitted an outside light... People don't want me traipsing round their house when all they want is a new light.

I explain it to them, but what do you do? I feel I am doing too much.
 
Im having a hard time following this POST, as it sounds so AGRESSIVE to me.

So you wouldnt bother with a R1+R2 or R2 Test to make sure there is Continuity on Earth before doing the Zs (which is Live)
Isnt a good idear to make sure there is a Earth before POWERING UP!
 
Wouldn't you have first established earth continuity on the existing circuit before making the alteration?
Are you that unsure of your work that you need to check the new conductors you have connected are actually connected, before energising?
 
I think the confusion may be the preliminary tests to establish the work you wish to do can be done safely does not require documentation as your just confirming the work you wish to do, but on completion of the work then a cert' is issued in the normal manner, that's how I read Spin's replies and that seems all correct to me. :)
 
To be honest the problem reported by the OP is not one I have ever experienced.
If I need to disconnect appliances from a circuit so I can test it, they get disconnected.
Never had anyone complain about me having to do so.
BS7671 requires us before undertaking an alteration or addition to first determine that the existing equipment (including the supplier's) and earthing arrangements are adequate for the proposed new work.
There is no requirement to issue any certification or a report when doing so.
Once new work is completed, appropriate certification along with the results of any relevant tests is required to be issued.

How people determine that the existing installation is adequate is up to them.
Some will want to test the complete installation, others just the circuit being altered.
With an RFC, I would suggest it's a good idea to first check that it is in fact an RFC, that there are no breaks in the ring, and depending upon the alteration, whether RCD protection will be required. if yes, then an IR test would be to my mind a good idea.
In the OP's case, there is no requirement for RCD protection.
As such all that will be required, is an MWEIC recording the IR of the new conductors, the Zs and that polarity is correct.
The Zs test will prove continuity of the CPC.

Lets CUT OUT some of this WORDY RUBBISH


AT no POINT did you make say you were checking the CPC was Connected before you TURNED it ON.


AS it says on the "MWEIC"
ESSENTIAL TESTS
Earth Continuity Satisfactory
Insulation Resistance L-L and L-E
Earth Fault Loop Impedance
Polarity satisfactory
RCD Operations

spose to make sure a circuit is OK before POWERING.

As far as i know all this POST was GOING ON ABOUT, was asking about is the IR results OK!!
 
To be honest the problem reported by the OP is not one I have ever experienced.
If I need to disconnect appliances from a circuit so I can test it, they get disconnected.
Never had anyone complain about me having to do so.
BS7671 requires us before undertaking an alteration or addition to first determine that the existing equipment (including the supplier's) and earthing arrangements are adequate for the proposed new work.
There is no requirement to issue any certification or a report when doing so.
Once new work is completed, appropriate certification along with the results of any relevant tests is required to be issued.

How people determine that the existing installation is adequate is up to them.
Some will want to test the complete installation, others just the circuit being altered.
With an RFC, I would suggest it's a good idea to first check that it is in fact an RFC, that there are no breaks in the ring, and depending upon the alteration, whether RCD protection will be required. if yes, then an IR test would be to my mind a good idea.
In the OP's case, there is no requirement for RCD protection.
As such all that will be required, is an MWEIC recording the IR of the new conductors, the Zs and that polarity is correct.
The Zs test will prove continuity of the CPC
.
This is one of the most pointless 'discussions' I've ever seen on this forum.
If a new addition is connected to an existing circuit then that circuit has been altered and should be tested AFTER the alteration to ensure compliance. What you are suggesting is testing only the addition PRIOR to connection, and testing the existing before any work takes place. This takes no account of a fault introduced when the addition is connected to the existing circuit!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Market Harborough

Thread Information

Title
IR Testing... Am I missing a trick here?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
49
Unsolved
--

Advert

Thread statistics

Created
uksparks,
Last reply from
Midwest,
Replies
49
Views
5,589

Advert

Back
Top