Carried out an EICR on an older installation at the start of the week prior to a mains board swap over. I had a low reading on one of the ring main IR tests, between live & neutral 0.02MOhms. I couldn’t see anything plugged in or switched on anywhere on the circuit & at that point I couldn’t gain access to the attic to see if there was anything that could affecting the test as the customer was away & it was locked. The live to earth was 150m Ohms, neutral to earth 185m Ohms. I swapped the mains over today & the circuit isn’t tripping the RCBO. If it was a fault in cable would that reading cause it to trip? Customer is home start of next week so can’t gain access to attic until then.
 
You could measure the continuity between L and N to help identify whether a load is connected or not.
You could also measure the current flowing through the circuit to establish whether something is connected.

Neither of these is infallible, but it will help you to understand what is going on.

An IR of 0.2Mohm between L and N is unlikely if the IR to earth is 150Mohm (I assume the m in the OP was supposed to be M)
 
The live to earth was 150m Ohms, neutral to earth 185m Ohms. I swapped the mains over today & the circuit isn’t tripping the RCBO. If it was a fault in cable would that reading cause it to trip?

It always puzzles me when an electrician asks this sort of question. We all learned ohms law at school, and use it regularly, and we all understand what causes an MCB, RCD, RCBO etc to trip so should be able to answer this.
The resistance between L and N is 0.02Mohms, which is 20,000 ohms, so you can calculate the current flow resulting from this using V=IR.
240/20,000=0.012A
So there will be 0.012A flowing between L and N.
Since that is significantly less than 32A no it won't cause the OCPD to trip.

Even if that was the IR to earth it wouldn't be enough to cause a 30mA RCD to trip.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
IR value on ring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
SSE,
Last reply from
davesparks,
Replies
6
Views
1,623

Advert

Back
Top