Hi,

Quick Q from a newbie. I had a NICIEC registered electrician install an isolation switch and extractor fan in my downstairs bathroom. I’m now replacing one of the down lights and found what is a surprising mess of wires in the false ceiling, all joined together with a terminal block (centre is neutral, left and right are live).

The grey cable leads to the isolation switch and the terminal block has been installed by the electricians. They’ve twisted the earth wire onto an existing twisted arrangement.

Is this safe/correct? I found it surprising from an Australian perspective but am open to being told that this is how things are done in Britain.

If this isn’t right, what should I do before adding the downloght? Put the terminal block in a junction box? Solder then sleeve twisted earthing wires?

My wife is back in an hour and I want everything back in the ceiling then, so prompt responses appreciated!

003C95EE-F332-4C1D-8622-5C8343E29349.jpeg


C3B358A2-435D-4924-8235-D501534F42AF.jpeg


1168CB1C-B024-486D-A8A0-5C1058A3C8FF.jpeg
 
Chris, it’s a 7.5kw induction hob that can be wired into a two phase supply, the idea I think being that by having each half of the job on a different phase, it’s a bit nicer to the DNO. I only have a single phase meter, so it’s necessary to bridge the wiring in the terminal block
on the hob.

My wife pointed out to me that the left two burners were giving an error message. I lifted out the hob and checked the wiring and found only one of the phase inputs had been connected (the rightmost connectors in the terminal block).

If this guy or madam is a qualified electrician, I will be a monkeys uncle and if you get a properly filled out certificate, I will eat my hat!
 
Hang on how do we know the spark did it? there may have been a feed hanging out from the ceiling and he just used that and didn't see the mess which was found when the OP was changing a light, if he did know then yes lets crucify him :D
 
Bathroom upgrades and extract fans seem to attract the very worst of the worst. Perhaps because householders plans often focus on the lowest cost quotes, and it's all about the cost of the marble tiles...
And it's not just electrics. - The quality of ductwork for airflow management and humidity can be just as horrifying. Out of sight, out of mind. I regularly need to "rescue" installations after bathroom fitters have left. Recent ones:

IMG_20180226_122749.jpg


IMG_20181005_094741.jpg
 
Cant beat an inline fan thrown across the loft.
To many cables for that JB, sleeking missing off some cpcs , Cable sheath outside JB, inline fan slung on joists as mentioned never could that have been done by an Electrician, if it was, then he/she wants to give up and stack shelves in Tesco, an utterly appalling job, needs reporting to trading standards, Watchdog, the mind does indeed boggle, to not incur the wrath of the Mods I'm not going to say what I'm thinking.
 
Without bringing anything to the party, I might be in danger of getting deleted here.

However, I'm not convinced that the OP is giving us the full story. Apologies OP if I'm incorrect.

Not withstanding the poor tradespersons that are out there, it doesn't take a expert to realise the state of the new installation falls way below of professional job.

If it were me I would not be allowing this so called electrician anywhere near my property & I would be concerned about the rest of the existing installation. I would be having an EICR conducted (wonder how the OP knows of this term?), and not repairing things myself. OP seems rather calm about things.

Perhaps I'm just getting too suspicious these days, having read similar threads. Getting as cynical as Murdoch :)
 
Thanks all; I've asked the electrician to come back to rectify the issues I've found. He is a busy guy, and I suspect that what happened is that he was so busy that he got a newly qualified/apprentice to do the work, and didn't have time to check it himself. I've also found an additional issue - a 45 amp cooker circuit on a 16 amp type B MCB.

As you've suggested, I'm going to get an EICR done by an electrician qualified to do commercial fixed wire testing. I'm hoping this won't be too intrusive given carpets and floors are down, but safety has to come first.

Midwest, I'm somewhat familiar with electrical installations, but not familiar with British domestic standards and common practice. To be honest, I'm only discovering most of the story/issues myself piecemeal as I look around the place.
 
I've said it before and I'll say it again.

Some cock ups are not the result of being untrained, they are simply the result of being a useless sod with low standards! Whoever twisted the CPCs together would have known it was not the professional way, regardless of whether or not they happen to be qualified and/or registered with a scheme. Most 12 year olds with no interest in electrical work whatsoever would be able to identify this as not the work of a pro!!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
Is this NICIEC extractor fan installation safe?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
41
Unsolved
--

Advert

Thread statistics

Created
David Thomas,
Last reply from
Deuce,
Replies
41
Views
5,327

Advert

Back
Top