It seems a little strange running two ring legs from the CU straight to the grid plate? Surely 1x 6mm will be exactly the same? I fail to see the difference apart from conductor size?
run a ring to a grid switch?
It seems a little strange running two ring legs from the CU straight to the grid plate? Surely 1x 6mm will be exactly the same? I fail to see the difference apart from conductor size?
Would you even get two 6mm conductors in? If its MK, crabtree or GET I could'nt do it.It seems a little strange running two ring legs from the CU straight to the grid plate? Surely 1x 6mm will be exactly the same? I fail to see the difference apart from conductor size?
What about in the event of a short circuit at the FCU?
Edit: Or a fault at the FCU that somehow results in 32A and no more being drawn through the 2.5mm cable?
Fire hazard me thinks
Wow, if I had a hat I would doff it to you nowWell according to Mk Data sheet 2x6mm is possible! Although i think looping with 4mm will be a better option and just having main feed as 6mm.
Im in near tears working on a 4 way grid in a 2.5mm RFC. What a spoon I am.Yes, thats what I refering to.Looking at Fig 15B Page.426 in BGB, on a 4mm radial protected by 30/32A OPD you can have an unfused spur run in 2.5mm.