Designing a kitchen appliance circuit, i plan to feed a bank of grid switches with a 6mm T&E fed via a 32A MCB, then each switch will have a 2.5mm cable to a fcu supplying an under counter appliance.
My main question is, is it ok to change down to 2.5mm and then feeding the FCU? As the cable cannot be overloaded as the main load is connected to the FCU at position?

Regards
 
come on I=P/U....you gonna try stuffin 4mm or 6mm into the back of an FCU?...lol...

i read it as 6mm to switch bank, then 2.5mm to each FCU. but doubt if could link switches in 6mm
 
telectrix yes that is a valid point! Maybe i will run a 4mm 20amp radial i will check the calcs!
I should have thought about that one damn! This is why you guys are good to run it through with!
 
so i take it hes in a commercial kitchen with lot of appliances and wants to switch them from the door.. so how would you go about this.

and detailed for the impaired glensparks;)
 
Why not run two seperate 2.5mm radials protected by two 20A breakers each feeding half of the switches within the grid then run your circuits in 2.5mm from each grid switch straight to each socket outlet? Also, no need for FCU's, unless the appliances have no plugs.
 
but what about the 2.5 from the switch to the fcu???
On this radial circuit that 2.5 run from the appliance switch can only ever be subjected to maximum 13a being drawn through it because the SINGLE appliance will be conected to the 2.5 via the FCU or a standard plug - either of which take a maximum 13a.
 
On this radial circuit that 2.5 run from the appliance switch can only ever be subjected to maximum 13a being drawn through it because the SINGLE appliance will be conected to the 2.5 via the FCU or a standard plug - either of which take a maximum 13a.

What about in the event of a short circuit at the FCU?

Edit: Or a fault at the FCU that somehow results in 32A and no more being drawn through the 2.5mm cable?

Fire hazard me thinks
 
Last edited:
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?
 
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?

I wasn't suggesting keeping the grid switch at all!
 
your 2.5 cable will be on a 32a mcb also the grid switch terminals are rated at 20amp again on a 32a mcb



you could run seperate 20amp radials and use a dp switch with neon and a un switched socket below your appliance will be fused in the plug that comes with it
 
Last edited by a moderator:
Yes sedgy34 but the switch is only supplying a 1x 13amp appliance so full load of 32a isn't flowing through the switch.
Sorry Murdoch misread you post, the client has stipulated a isolation bank of switches.
 
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?

Why not ?

If the grid assembly is the only outlet on that circuit,the ring will be almost perfectly balanced

I would say keep it simple 2,5mm ring to the grid assembly on its own 32A mcb,
If you want ,you can fit grid fuses as well for the loads and outlet plates for the appliances

I would also suggest the 20 amp rating refers to the switch contacts not the supply terminals
 
Last edited:
It seems a little strange running two ring legs from the CU straight to the grid plate? Surely 1x 6mm will be exactly the same? I fail to see the difference apart from conductor size?
 
I gather the whole idea that the switch supplies x amount of points but why run 2x 2.5mm 20m to the grid whereas 1x 6mm will be more than adequate?
 
It seems a little strange running two ring legs from the CU straight to the grid plate? Surely 1x 6mm will be exactly the same? I fail to see the difference apart from conductor size?

Do 2 installations,one with a 6,0mm radial supply and another with 2,5mm ring.fit the grids then decide which was the easiest and better quality arrangement
 
Well according to Mk Data sheet 2x6mm is possible! Although i think looping with 4mm will be a better option and just having main feed as 6mm.
 
You have had many opinions, so all I can now say is, everyone to their own ways, hope it works out for you

I will think of this thread the next time I'm putting those little loops across the grid switches
icon12.png
 
What about in the event of a short circuit at the FCU?

Edit: Or a fault at the FCU that somehow results in 32A and no more being drawn through the 2.5mm cable?

Fire hazard me thinks

OK - I'm not tring to be contentious here - I'm sure you are more experienced than me; but are you saying that my reply is incorrect? I was thinking say for example on a 32a radial in 4mm T&E. You are permitted to spur off to one double socket in just 2.5mm T&E. We are not suggesting that 2.5mm will be ok at 32a.
Happy to be corrected so long as it's constructive.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Kitchen Appliance circuit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
61
Unsolved
--

Advert

Thread statistics

Created
Snapester,
Last reply from
telectrix,
Replies
61
Views
8,810

Advert

Back
Top