Designing a kitchen appliance circuit, i plan to feed a bank of grid switches with a 6mm T&E fed via a 32A MCB, then each switch will have a 2.5mm cable to a fcu supplying an under counter appliance.
My main question is, is it ok to change down to 2.5mm and then feeding the FCU? As the cable cannot be overloaded as the main load is connected to the FCU at position?

Regards
 
come on I=P/U....you gonna try stuffin 4mm or 6mm into the back of an FCU?...lol...

i read it as 6mm to switch bank, then 2.5mm to each FCU. but doubt if could link switches in 6mm
 
telectrix yes that is a valid point! Maybe i will run a 4mm 20amp radial i will check the calcs!
I should have thought about that one damn! This is why you guys are good to run it through with!
 
Why not run two seperate 2.5mm radials protected by two 20A breakers each feeding half of the switches within the grid then run your circuits in 2.5mm from each grid switch straight to each socket outlet? Also, no need for FCU's, unless the appliances have no plugs.
 
but what about the 2.5 from the switch to the fcu???
On this radial circuit that 2.5 run from the appliance switch can only ever be subjected to maximum 13a being drawn through it because the SINGLE appliance will be conected to the 2.5 via the FCU or a standard plug - either of which take a maximum 13a.
 
On this radial circuit that 2.5 run from the appliance switch can only ever be subjected to maximum 13a being drawn through it because the SINGLE appliance will be conected to the 2.5 via the FCU or a standard plug - either of which take a maximum 13a.

What about in the event of a short circuit at the FCU?

Edit: Or a fault at the FCU that somehow results in 32A and no more being drawn through the 2.5mm cable?

Fire hazard me thinks
 
Last edited:
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?
 
your 2.5 cable will be on a 32a mcb also the grid switch terminals are rated at 20amp again on a 32a mcb



you could run seperate 20amp radials and use a dp switch with neon and a un switched socket below your appliance will be fused in the plug that comes with it
 
Last edited by a moderator:
Yes sedgy34 but the switch is only supplying a 1x 13amp appliance so full load of 32a isn't flowing through the switch.
Sorry Murdoch misread you post, the client has stipulated a isolation bank of switches.
 
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?

Why not ?

If the grid assembly is the only outlet on that circuit,the ring will be almost perfectly balanced

I would say keep it simple 2,5mm ring to the grid assembly on its own 32A mcb,
If you want ,you can fit grid fuses as well for the loads and outlet plates for the appliances

I would also suggest the 20 amp rating refers to the switch contacts not the supply terminals
 
Last edited:

Reply to Kitchen Appliance circuit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock