Why not run two seperate 2.5mm radials protected by two 20A breakers each feeding half of the switches within the grid then run your circuits in 2.5mm from each grid switch straight to each socket outlet? Also, no need for FCU's, unless the appliances have no plugs.
but what about the 2.5 from the switch to the fcu???
On this radial circuit that 2.5 run from the appliance switch can only ever be subjected to maximum 13a being drawn through it because the SINGLE appliance will be conected to the 2.5 via the FCU or a standard plug - either of which take a maximum 13a.
What about in the event of a short circuit at the FCU?
Edit: Or a fault at the FCU that somehow results in 32A and no more being drawn through the 2.5mm cable?
Fire hazard me thinks
How about the good old 2.5mm T&E ring protected by a 32A breaker in the board. Got to be easier!
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?
I wasn't suggesting keeping the grid switch at all!
your 2.5 cable will be on a 32a mcb also the grid switch terminals are rated at 20amp again on a 32a mcb
you could run seperate 20amp radials and use a dp switch with neon and a un switched socket below your appliance will be fused in the plug that comes with it
Yes sedgy34 but the switch is only supplying a 1x 13amp appliance so full load of 32a isn't flowing through the switch.
Sorry Murdoch misread you post, the client has stipulated a isolation bank of switches.
Why not ?
If the grid assembly is the only outlet on that circuit,the ring will be almost perfectly balanced
I would say keep it simple 2,5mm ring to the grid assembly on its own 32A mcb,
If you want ,you can fit grid fuses as well for the loads and outlet plates for the appliances
I would also suggest the 20 amp rating refers to the switch contacts not the supply terminals
i'm with des and murdoch here. 2.5mm RFC to grid. as in K.I.S.S.