Incorporate general sockets too, if required.Why not just run a Ring in 2.5? even if it is only to the grid switch it will be hell of a lot easier to terminate. You could keep it on a 32A Breaker then.
Incorporate general sockets too, if required.Why not just run a Ring in 2.5? even if it is only to the grid switch it will be hell of a lot easier to terminate. You could keep it on a 32A Breaker then.
On this radial circuit that 2.5 run from the appliance switch can only ever be subjected to maximum 13a being drawn through it because the SINGLE appliance will be conected to the 2.5 via the FCU or a standard plug - either of which take a maximum 13a.but what about the 2.5 from the switch to the fcu???
On this radial circuit that 2.5 run from the appliance switch can only ever be subjected to maximum 13a being drawn through it because the SINGLE appliance will be conected to the 2.5 via the FCU or a standard plug - either of which take a maximum 13a.
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?
There was an article in NICEIC mag about putting grid switches on ring and how it needs to be balanced at the middle of the ring, i will see if i can dig it out! Also the grid switch is one point so i wouldn't want to run a ring to one point?
run a ring to a grid switch?