If a ring main is needed to be installed with one leg of the ring passing through a stud wall with thermal insulation (Inst. method 103#) the current carrying capacity is 13.5A. To comply with regs on a ring final circuit, the current carrying capacity has to be at least 20A for a 32A breaker. Can i protect this circuit on a 20A breaker and still comply with regulations? My thinking is that if you devide 32 by 20 (which is 1.6 (call this the 'factor')) then you need each leg to be capable of carrying at least 12.5A.
Im sure im not the only one to come accross this so any help would be much appreciated.