sparkymaz

If a ring main is needed to be installed with one leg of the ring passing through a stud wall with thermal insulation (Inst. method 103#) the current carrying capacity is 13.5A. To comply with regs on a ring final circuit, the current carrying capacity has to be at least 20A for a 32A breaker. Can i protect this circuit on a 20A breaker and still comply with regulations? My thinking is that if you devide 32 by 20 (which is 1.6 (call this the 'factor')) then you need each leg to be capable of carrying at least 12.5A.

Im sure im not the only one to come accross this so any help would be much appreciated.
 
why is the stud wall insulated? (internal wall so no heat loss- common area so no real need for any major sound proofing?) easiest solution would be to remove insulation in the section you run cable (i would) rather than have a kitchen ring on 20a as this would normally be biggest load.
rather than downgrade the mcb i personally would sooner upgrade the cable or alter the reference method ie, singles in conduit through stud wall section.
 
yeah i know what your saying with changing the installation method. all walls are insulated now days. The biggest pain in the arse for us all i reckon. Its just hyperthetical really. Got my elecsa assessment soon. but when doing a new installation, say the main cable route has thermal insulation exceeding 100mm in thickness, (ref 101, table 4D5). This means 16mm would have to be used for a 9.5kw shower. Seems excessive to me but hey i dont write the regs.

Also, the thermal insulation would be installed after the 1st fix on the electrics. Just seems that we are going in the direction of using 4mm for ring mains, as on a new installation when are we ever going to avoid any insulation at all? even if we do, how do we know it aint gonna get crammed with insulation when we have finished the 1st fix? Is it feasible to create a system where we can keep the main cable routes free of insualtion by building a compartment within the joist layouts. Or would this contravene building regs with inadequate insulation?

Would love to hear your guys thoughts
 

Reply to Kitchen ring circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
602
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi there I am struggling with the following calculation. 4mm Ring Final Circuit, In = 32A Cg - group of 6 with a correction factor of 0.57 Ci -...
Replies
10
Views
1K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
715
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock