How may LED lamps and dimmers? Are they all supplied by the one MCB - what rating and type? What else does this MCB supply and is/are it/they on when the LED flickering and buzzing happens? Could you measure mains voltage when flickering and when not flickering please. Any high kW resistive or motor loads being turned on/off correlated with lamp flickering? If you have say only half the number of LED lights on does the flickering stop? Does flickering occur at all dimmer knob settings? Please confirm the buzzing is from an MCB and not an RCBO or
How may LED lamps and dimmers? Are they all supplied by the one MCB - what rating and type? What else does this MCB supply and is/are it/they on when the LED flickering and buzzing happens? Could you measure mains voltage when flickering and when not flickering please. Any high kW resistive or motor loads being turned on/off correlated with lamp flickering? If you have say only half the number of LED lights on does the flickering stop? Does flickering occur at all dimmer knob settings? Please confirm the buzzing is from an MCB and not an RCBO or RCD. What do LED and dimmer manufacturer instructions say about number of LEDs which can be controlled at same time by a dimmer?
Hi,its the correct dimmer switch, only 60W eorth of dimmers on a 150 w dimmer...it has a complete separate feed supplying only this...no loose connections...it just happens randomly and the arc sound is in the fuseboard...alll connections are sound...ive swapped the rcds and MCBS but still happening! Really starnge...voktage etc is bang on...the whole I installation is brand new and only drawing 28 amps with everything on...
 
If I understand the situation you have a 4 gang grid with 4 dimmers flush to the wall controlling 4 sets of lights (All LED?). It may be the dimmers are becoming too warm because of mutual heating and little cooling. So, what I would do is unscrew the securing screws and lift the switch plate away from the wall to allow some air to flow and see if it has any beneficial effect on stopping the flicker. The situation would be exacerbated of the 4 dimmers are stacked vertically rather than in a row horizontally - so you could try rotating through 90 degrees . I leave it to you to do this safely so fingers cannot touch live parts - maybe use a surface box as a spacer which has some small holes drilled regularly into the top/bottom/left/right sides. The long term solution can follow if overtemperature is the cause.

I wonder/muse whether the dimmer electronics start to miss some LED drive cycles in a burst - so to the eye the LEDs do go off completely and on again repetitively - ie: flicker - as a way of indicating overload/overheat or perhaps because a safety feature starts to kick in to reduce thermal runaway leading to complete failure of the electronics.

The CU 'arcing' noise is perhaps then the lower than mains frequency buzz made by the mcb's solenoid as it responds magnetically to the burst of on/off LED drive current through it.
 