Then it would trip the RCD every time it was switched on.

Though it is worth noting that it is a 3 gang switch, and the op hasn't categorically stated whether its the one same switch that's operated which causes the trip each time. So it could well be a light that is less often used which when switched on trips the RCD. This could indicate a borrowed neutral problem.

To the O.P,

Is it just one of the switches on the 3 gang switch which causes the trip or does it trip randomly with any one of the 3?
The reason I ask is that to determine where the fault lies there are processes of elimination to go through. It can be sometimes difficult to pin down the cause of random tripping without eliminating the obvious first.
 
Last edited by a moderator:
It also could be a lighting cable that as rubbed againts a socket cable when they were installed ,with the neutrals almost touching together and the insulation broke down it could course the intermittent fault coursing the rcd to trip , but this is just a idea as said the only way to find out is test out the circuits
 