I would guess a IR test was missed due to the CPC's & neutrals cross connected at some of the fittings !
i didn't install these fittings that is why I locked it off ready for tomorrow and will rectify and carry out the appropriate tests then, thanks for the feedback
 
I realised that Tommy from post 9 as the 6 faulted lights had nothing to do with the 60 you had fitted! You only have to get the other 4 out as you have already removed 2 finding the CPC Neutral faults. It is obvious that no testing was carried out with regards these lights and I would document my findings on the new certificate backed up with photos of the faults that you trace when you submit your invoice! Let us know what you find !
 
Oh, and disconnect l,n and cpc for continuity tests. Reconnect cpc only for IR tests
what you on about now here eh?
use the wander lead, connect at the origin of supply and start going from point to point watching the values as you go....when its shot up you know the high resistance joint was at the last point tested...
 
what you on about now here eh?
use the wander lead, connect at the origin of supply and start going from point to point watching the values as you go....when its shot up you know the high resistance joint was at the last point tested...

That might work, or might be misleading. It might be a bad connection to L or N. it might be a low IR between L or N or E. so verification of R1 R2 and Rn first, with any parallel paths disconnected as far as possible, then IR tests, but with the cpc connected to include any parallel paths.
 
think what glenn was suggesting was to wander lead each conductor in turn, L,N, (& E) to find the point of high resistance.
 
I agree with the method, I'm just saying that if its an IR problem that method might not indicate the fault and also that if it does iR test anyway after continuity test as it doesn't sound like this install has been tested in the first place.
 