Hi wonder if anyone can help me.
Got a call from village hall caretaker saying lights have started tripping fuse this week.
Popped there today to have a quick look incase it was something simple but will have to return tomorrow.

What we have is 2 rows of 5 grid fluorescents (4 x 36w) in each fitting, they are on a 6A MCB (no RCD protection).
They have been installed 3 years ago and all wiring etc looks to be in good condition although I'm yet to IR the circuit as it would have meant disconnecting all 10 fittings.

If my calculations are correct the 6A circuit should carry 1440watts and the fluo's add up to exactly the same figure (36w x 4 x 10).
There is small buzzing noise coming from DB only when this MCB is turned on, no loose connections in DB

Lights are working fine and then randomly trip after a period of time, although they didnt to so during half hour or so i was there today.

Just wondering if anyone has any ideas to save me a bit of time tomorrow!
clearly circuit is very close to overloading but if this is the case why has it taken 3 years to happen, or maybe something has started breaking down in a fitting (ballast?).
Thanks in advance.
 
I would say that the circuit breaker has been run close to the load for a long time and has now become a bit too sensitive.
I am quite surprised that it has managed to stay in when starting the fluorescent load unless they are staged switched.

However it would be a good idea to check for lighting faults as well, generally the ballast will break down or the lamps have failed and are trying to start continuously, putting more strain on the MCB.

Clamp the supply cable and see what current is actually being drawn as there can be significant losses with fluorescent lighting, it may be that you are above 9 amps in which case it is doing its job!
 
as above. check the circuit first and then, depending on the current measured and the cable size (allowing for installation method), consider fitting a 10A type B or a 6A type C. in any case replace the breaker.
 
cheers guys good advice. it is wired in 1.5mm and the two rows are switched separately therefore I don't believe start up current is the issue, so dont think a type c breaker will help but certainly a 10A type B MCB could be the answer. Will test the circuit properly tomorrow and take it from there.

Any idea what would be causing this buzzing noise? the MCB itself maybe?
 
Last edited by a moderator:
could well be. if it has tripped on o/l a good few times, or if it's running close to it's limit.
 
only if wanting to IR test L-N. a breakdown in insulation between these could lead to excessive current being drawn.
 
so that I don't send 500v through any components in the fluo's that could end up fried! granted i could test IR at 250v, but none the less I didn't have the time today it was just a flying visit incase it was a quick fix fault
 
Seen this many times, you can either fit 10A or drop some tubes out, i have had to do both on separate occasions. When you clamp it, unless they are HF fittings, and all tubes lit you will be between 8 and 9 amps.
 
cheers plugsandsparks, will stick a clamp on ammeter tomorrow. Looks like no thought has gone into the loading, just the usual case of 'lighting circuit - stick it on a 6amp MCB'
 
If you disconnect the fittings or unplug the roses you will IR test only part of the job. The fittings are part of the installation.
L and N joined together and tested to earth will eliminate any earth faults ( wiring and fittings) and not damage the fittings. Start on 250v if you like. Testing this way also shows up any crossed N and E connections at the fittings ( seen it many times, guys on autopilot).

Boydy
 
L and N joined together and tested to earth will eliminate any earth faults with out damaging the fittings that I agree with.

But I was always taught to disconnect all light fittings and remove all lamps from the circuits, was the correct way to test the wiring as that is all you are testing not the fitting, unless it is fault finding they should not be in the circuit?

Fault finding in flus is something i have always struggled with unless they are completely short circuited its a nightmare, why they stopped fitting fuses I can never understand ?
 
arguably, if the fittings are on flex to plug-in roses, they are not part of the fixed wiring.
 
L and N joined together and tested to earth will eliminate any earth faults with out damaging the fittings that I agree with.

But I was always taught to disconnect all light fittings and remove all lamps from the circuits, was the correct way to test the wiring as that is all you are testing not the fitting, unless it is fault finding they should not be in the circuit?

Fault finding in flus is something i have always struggled with unless they are completely short circuited its a nightmare, why they stopped fitting fuses I can never understand ?