T
tbs1983
Hi wonder if anyone can help me.
Got a call from village hall caretaker saying lights have started tripping fuse this week.
Popped there today to have a quick look incase it was something simple but will have to return tomorrow.
What we have is 2 rows of 5 grid fluorescents (4 x 36w) in each fitting, they are on a 6A MCB (no RCD protection).
They have been installed 3 years ago and all wiring etc looks to be in good condition although I'm yet to IR the circuit as it would have meant disconnecting all 10 fittings.
If my calculations are correct the 6A circuit should carry 1440watts and the fluo's add up to exactly the same figure (36w x 4 x 10).
There is small buzzing noise coming from DB only when this MCB is turned on, no loose connections in DB
Lights are working fine and then randomly trip after a period of time, although they didnt to so during half hour or so i was there today.
Just wondering if anyone has any ideas to save me a bit of time tomorrow!
clearly circuit is very close to overloading but if this is the case why has it taken 3 years to happen, or maybe something has started breaking down in a fitting (ballast?).
Thanks in advance.
Got a call from village hall caretaker saying lights have started tripping fuse this week.
Popped there today to have a quick look incase it was something simple but will have to return tomorrow.
What we have is 2 rows of 5 grid fluorescents (4 x 36w) in each fitting, they are on a 6A MCB (no RCD protection).
They have been installed 3 years ago and all wiring etc looks to be in good condition although I'm yet to IR the circuit as it would have meant disconnecting all 10 fittings.
If my calculations are correct the 6A circuit should carry 1440watts and the fluo's add up to exactly the same figure (36w x 4 x 10).
There is small buzzing noise coming from DB only when this MCB is turned on, no loose connections in DB
Lights are working fine and then randomly trip after a period of time, although they didnt to so during half hour or so i was there today.
Just wondering if anyone has any ideas to save me a bit of time tomorrow!
clearly circuit is very close to overloading but if this is the case why has it taken 3 years to happen, or maybe something has started breaking down in a fitting (ballast?).
Thanks in advance.