went to a job today customer said lights kept tripping Main RCD, only 5 Fluorescent on the circuit all in one room( its a portakabin) so i have 5 lights and 2 pir on the Circuit

I get there lights are fine turning off on many time( turned PIR down to lowest setting) so they would constantly go on and off done for about 10mins to trip, left them for about 2 hours went back as i walked the PIR picked me up i seen the Starters light up then before the lights came on the Main RCD tripped so i check all connection fine

the fault is not happening quick enough for me to disconnect each light 1 at time and check which light in tripping also look fine, I was thinking of changing all the starters

all the ballast also looked OK, the PIR where also Brand new
 
maybe some inherent leakage on the installation and the lights are just taking it over the threshold.
 
Did you test the rcd in any way. Personally I would have put a tong on it and at least ramp tested it.
 
there nothing else really on the board 2* convector heaters that are also brand new and 1 water heater with nothing plugged in to the sockets
 
Seen this before , momentary loss off neutral when florries start after the capacitors have discharged, you could change rcd to a type s , time delayed if possible
 
Seen this before , momentary loss off neutral when florries start after the capacitors have discharged, you could change rcd to a type s , time delayed if possible
But then as it is a temporary supply you may be breaking regs regarding protection of socket outlets by rcd. I am not sure a time delay will be adequate for sockets under temporary conditions.
 
agree ^^^^^. might be an idea to take the lights off the RCD if it's not an up front device.
 