Where did you find the current/time plot for the BS1362 fuses? I have not seen that in any (obvious) place the few times I looked.
Maximum Zs for a 13 amp bs1362 fuse is 2.30 ohms 0.4 disconnection time , table 41.2
For a 5 second disconnection time it is 3.64 ohms table 41.4
Or 13 x 1.45= 18.85 amps
[automerge]1587045045[/automerge]
Where did you find the current/time plot for the BS1362 fuses? I have not seen that in any (obvious) place the few times I looked.
Maybe try this ABE79CF9-A864-437C-A456-25BDF8BCD157.png
 
Last edited:
I just think it's always good practice for the OCPD to be rated lower than the ccc of the circuit cable,regardless of the 'fixed load' and it's no bother in a loft /outbuilding or similar to fit a sfcu instead of just a normal light switch. Always done it this way and I see no reason to change now.
Coz we are old school Dave.
 
Sometimes you need to simplify things I say. Is adding an FCU before a light switch make the situation dangerous. No? Does it break any regulations? No. Would it make sense to a future electrician? Sure, even if they don't agree with it. So therefore it's not worth worrying about IMO.
 
Sometimes you need to simplify things I say. Is adding an FCU before a light switch make the situation dangerous. No? Does it break any regulations? No. Would it make sense to a future electrician? Sure, even if they don't agree with it. So therefore it's not worth worrying about IMO.
Indeed, it is a very minor point. But I enjoy chatting carp about the minutiae of our trade
 
Indeed, it is a very minor point. But I enjoy chatting carp about the minutiae of our trade

Oh absoloutely (I can get into pretty boring in depth detail about 13a plugs!) I just felt it a point worth mentioning. I'm guilty of getting wrapped up in thought on a job and often find myself having to strip it back a bit when in a job situation.
 

Reply to Lighting from fused spurs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K
Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Replies
9
Views
1K
Hi all, I have recently bought a house. The garage is at the end of the garden and has a double socket. The socket is on the ring and not a spur...
Replies
1
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all, Looking for some tips on supplying my pool equipment (2kw heater, 1hp pump, 1.6kw swim jet, 12w led light) with power. My house has a...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock