Hi all. Just wanted to resurrect this one as I've found something in the regs that would mean a 13A BS1362 fuse may not be appropriate for protecting lighting in many cases, and wouldn't have been suitable in this instance. It's to do with the co-ordination between conductor and overload protective device.

433.1.1
The operating characteristics of a device protecting a conductor against overload shall satisfy the following conditions:
...
(iii) the current (I2) causing effective operation of the protective device does not exceed 1.45 times the lowest of the current-carrying capacities (Iz) of any of the conductors of the circuit.

For a 13A BS1362, it appears I2 is 26A.

26/1.45 = 17.9A

So for 1mm² T+E, the 13A fuse would not comply in any case, and for 1.5mm², it would only comply if ref. method C.

View attachment 57198
A single light or lights wouldn’t necessarily require overload protection by nature of the load fed from a fused spur
 
Hmm. There's certainly a few sides to this. I must admit on the odd occasion I've been in situtions like this (for example in my own under stairs cupboard) I have taken a 13a FCU from adjacent RFC > 2x Sockets > 5a SWFCU acting as the light switch itself.

I think for me, in that instance it just acted as 'neat' way of changing conductor sizes down to the 1mm I used for the light. And just because it seemed logical. The source FCU was some distance away, it may "look wrong" if someone were to see a light fitting coming straight off the back of a socket (albeit fused 13a at the source FCU). The FCU for me acted more as a light switch and differentiation point.
 
I just think it's always good practice for the OCPD to be rated lower than the ccc of the circuit cable,regardless of the 'fixed load' and it's no bother in a loft /outbuilding or similar to fit a sfcu instead of just a normal light switch. Always done it this way and I see no reason to change now.
 
Where did you find the current/time plot for the BS1362 fuses? I have not seen that in any (obvious) place the few times I looked.
Maximum Zs for a 13 amp bs1362 fuse is 2.30 ohms 0.4 disconnection time , table 41.2
For a 5 second disconnection time it is 3.64 ohms table 41.4
Or 13 x 1.45= 18.85 amps
[automerge]1587045045[/automerge]
Where did you find the current/time plot for the BS1362 fuses? I have not seen that in any (obvious) place the few times I looked.
Maybe try this ABE79CF9-A864-437C-A456-25BDF8BCD157.png
 
Last edited by a moderator:
I just think it's always good practice for the OCPD to be rated lower than the ccc of the circuit cable,regardless of the 'fixed load' and it's no bother in a loft /outbuilding or similar to fit a sfcu instead of just a normal light switch. Always done it this way and I see no reason to change now.
Coz we are old school Dave.
 
Sometimes you need to simplify things I say. Is adding an FCU before a light switch make the situation dangerous. No? Does it break any regulations? No. Would it make sense to a future electrician? Sure, even if they don't agree with it. So therefore it's not worth worrying about IMO.
 
Sometimes you need to simplify things I say. Is adding an FCU before a light switch make the situation dangerous. No? Does it break any regulations? No. Would it make sense to a future electrician? Sure, even if they don't agree with it. So therefore it's not worth worrying about IMO.
Indeed, it is a very minor point. But I enjoy chatting carp about the minutiae of our trade
 
Indeed, it is a very minor point. But I enjoy chatting carp about the minutiae of our trade

Oh absoloutely (I can get into pretty boring in depth detail about 13a plugs!) I just felt it a point worth mentioning. I'm guilty of getting wrapped up in thought on a job and often find myself having to strip it back a bit when in a job situation.
 