Discuss Live tests on Economy 7? in the UK Electrical Forum area at ElectriciansForums.net
DNS1
It may be completely stupid but I've been wondering about this one for a while...
Short of coming back at night, how do I get Ze or do the RCD testing for an economy 7 system?
Last one I did had no seals on the clock so I just advanced it. Otherwise a set of leads from the main CU, this will change the results slightly but should be for the worse so if they are OK you should also be OK on the proper tails.
I recently fitted a CU for Econ 7 which was not yet connected.
I took a live feed from the main CU with 10mm just to do the tests then connected the 25 mm tails for the DNO to connect when they changed the meter!
Dead tests would be OK for your certificate calculating the ZS. (But then your RCD needs testing)
ZE would be taken as you would normally do it at the premises!
Stay over night with the customer ;)
I think you mean Zs? As said I'd run some temporary tails to test and note the certificate accordingly. If minor job calculate Zs
Reply to Live tests on Economy 7? in the UK Electrical Forum area at ElectriciansForums.net
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Yesterday moved my Mum into her new bungalow. The Hortsmann had been off for a few months I suspect. The boost worked, but nothing happened...
I am asking on behalf of a friend who has an outbuilding that he uses as an art studio, the building is fully insulated and is currently heated by...
Been round to a house to quote to replace some storage heaters for new panel heaters and came across a strange (to me at least) way of wiring the...
4K
I get asked quite a lot about replacing old storage heaters with something more economical and I don't know what to recommend. Some people ask for...