Personally I find it hard to see how the RMU could be tripped by a MCB fault. At, say, 10kA MCB breaking limit (as I assume the related panel has a lower PFC...) that is just 3x the ACB's rating so it ought to be well under the HV side protection threshold.

So either the HV side is broken or very badly configured (which you would think would have been noticed when previously in use), or that MCB's circuit is somehow upsetting it via a control signal or somehow tricking it in to thinking there is an earth-fault or similar.
 
Update on this, we have found out that there is a small panel within the switchroom that is connected to the RMU, no one on site knew about this and the guy that attended the initial fault and reset the RMU didn`t know either. It looks like a power supply with batteries but it is not labelled and is at the opposite end of the switchroom from the RMU. We have assumed that the feed to this has been cut and when the batteries discharged the trip occurred. However, it has been off for a while now and not tripped since. We have installed a new supply to the panel but leaving it off until the specialist can confirm what it does. He was due yesterday but didn`t turn up. The 63A MCB was causing the trip but only because it supplied the DB that supplied the panel in the switchroom.
Thanks for all comments and advice
 