Change the lock on the door and see if it magically stops tripping!

And posting up some pictures on here would be good, but do expect a little light ribbing if it turns out to be an RCD and not a switch ;)


Sent from my iPad using Tapatalk
 
No murdoch not mA. The main switch on the board is rated 100A. This operates aswell as the rcbos. I agree i havnt given enough to go on. Will be going back so will get some snaps etc. Apparantly the rewire was down to the current problem. Obviously the problem was never solved.

Think Murdoch means is the Main Switch a 100A 100mA rcd, someone asked does this Main Switch have overload settings?
 
Its very strange, you would assume that a full re-wire would include replacing all protection devices and include a new main switch in the new CCU??
If the installation has been tested correctly and is satisfactory then one would assume that it is an appliance or accessory causing the problem??

You'd hope so, but then thorough testing should have revealed where the fault was. Unfortunately some people don't work like this though, instead resorting to going though the installation trying changing everything they can to see if that does it.

If everything is on RCBOs you'd expect a faulty appliance or accessory to only trip that circuit, and certainly not the 'main switch'.

Without having seen the installation I can't help thinking either some local scallywags are sneaking in and making a nuisance of them selves, or old Mrs Miggins who looks after the shop on a Wednesday afternoon feels more comfortable turning everything off before she locks up.
 
Curveball - maybe someone had a 100amp double pole mcb in the totty bag (as we all do naturally) and wanted to replace the original rcd that came with the board.

Thinking outside the box and all that

Sent from my SM-G920F using Tapatalk
 