In a TN-S if copper the protective bonding conductors need not exceed 25mm2.just wondering what you guys reckon.
Main Earth tns,95mm conductors,50 mm Earth,bonding conductor 35 mm.
Sub main to other building,Swa 70 mm 4 core ,c/w 35mm Earth conductor.
Main bonding required in building to usual utilities,what code would you give.
Nope.Yea it's a Eicr,bonding is present but not to the size needed.
Thinking all earth's need to be sized to the intake position,exporting the main Earth to the building,meaning a 50 mm Earth cable.
Bonding conductors need to be connected back to the MET to which there is only one.Yea,so where would you connect the bonding conductors,25mm being correct.
Yes agree,but wondering about the other sub mains running from that MPDB,Earth can be used for main bonding,but originally installed for main Earth.Quite simple this your main protective bonds need not exceed 25.0 and a separate 35.0 earth has been installed, I see no problem.
Did you get that motor running Cliff.
Cpc half the swa,35 mm,bonding needs to be 25mm.Bonding conductors need to be connected back to the MET to which there is only one.
An cpc can be used as a combined bonding conductor and cpc if it satisfies both requirements what size does the cpc actually need to be and what size do the bonding conductors need to be.
You could calculate what actual size the main earthing conductor needs to be from the Adiabatic equation and work out that the bonding conductors need only be not less than half required size and not less than 6mm
I would say the existing 35mm can be used as both so in the other building the extraneous parts are bonded back to the db containing the 35mm conductor with in turn is connected to the MET.
Your swa armour size is irrelevant if it's not being used as a cpc, you are just supplementary bonding the swa to earth as it's an exposed conductive part.Cpc half the swa,35 mm,bonding needs to be 25mm.
Agree what you say,but there are other Db's in that area,supplied by swa cables,does that the interfere with those main earth's,if using that 35 mm for main bonding.
The actual main Earth is 50 mm,hope I've explained myself ok.
Yes.Yea I see,meaning the 35 mm complies with that installation,bonding conductors can be installed at that point,these will be 25 mm,thanks.