When we are asked to change a CU i have been told on pme and tns the main earthing conductor is the responsibilty of the electricity board.
so if this is the case why is a 16 mm earth sold on packs of 2meter tails?,
example change board 25mm tails or 16mm if 80amp main fuse 10mm to gas and water but only sometimes 4 or 6 mm main earth do we just record this on an EIC
Cheers
Pretty pointless exercise then, to have an earth rod that's not buried!! lol!!!
I know your taking the **** - its driven into the ground but the top is exposed - therefore not buried and not protected against mechanical protection - regs states 25mm - I cant be bothered to get OSG or BGB out for the Reg number
Upvote 0
Burry it it's not hard ! Drill , then get good old lumpy out for that bit your drill won't do!
It is when someone has put a concrete path around it - I have a SDS with a Rod driver attachment but that wont drive it past the concrete
Upvote 0
Nicholas I think you have mis-read the OSG.
it says min 25mm if buried but not protected against corrosion
2.5mm if not buried but protected against corrosion and mechanical damage,
4mm if not protected and not buried
Upvote 0
Nick,if the earth conductor is protected against corrosion, its not buried,its not mechanically protected,then 10.0mm is ok
542.3.1
I usually use 10mm Des, seeing as how I carry that size anyway.
Upvote 0
More to the point, how do you terminate 25mm into a domestic CU ?, unless it get's a 'haircut' (Geordie sparks term LOL)
Upvote 0
542.3.1:
Protected against corrosion and mechanical = 2.5mm copper
Protected against corrosion and not mechanical = 16mm copper
Not Protected against corrosion and not mechanical = 25mm copper
Most properties in Pembrokeshire with TT are not protected against corrosion or mechanical protection so must be 25mm
To terminate 25mm into a CU is a pain I had to split the cable to 4/3 wires and terminate that way over 2 connections - NAPIT said that was the best way
Upvote 0
542.3.1:
That reg refers to the cable being buried directly in the ground, see the extract from the OSG I posted earler
Upvote 0
Either way in Pembrokeshire its not possible because all the rods have been concreted to make a path - i will take the trunking idea into consideration next time
Upvote 0