I inherited a BnQ job. Not my choice but still going strong 2 years after I got it. (I removed all B&Q references on it!!)
 
I have the socket and see one that does RCD and EARTH as well,one thing I would say is whichever one you buy make sure it has 3 green lights for correct,some do different combinations and it could get confusing,one make has centre and right for ok and centre and left means a fault, the warble tone is good too especially if you cannot see the socket,behind a cupboard for instance.
 
Socket testers have there place in an electricians test kit, and can be useful as an indicator of possible problems on a socket circuit. But RCD and earth loop impedance testing with these things isn't one of them, the add-ons are more of a gimmick than anything else.

All you need, is a bog standard socket tester, preferably one with an audible facility. The rest of them leave well alone. ...You should have the correct test equipment, to conduct RCD/ELI tests professionally....
 
All you need, is a bog standard socket tester, preferably one with an audible facility. The rest of them leave well alone. ...You should have the correct test equipment, to conduct RCD/ELI tests professionally....
unless you work for british gas
​
 
All you need, is a bog standard socket tester, preferably one with an audible facility. The rest of them leave well alone. ...You should have the correct test equipment, to conduct RCD/ELI tests professionally....

unless you work for british gas


Well they are like the NICEIC these days, ...they like making up their own rules!! lol!!



​
 
I bought mine as it was handy just to keep an eye on socket earths before using the sockets,if you just want to know a socket is safe to use then its good,never know what you could be plugging into otherwise.Incidentally I contacted the maker to see the resistance values and was quite pleased,much better than a standard tester
I have looked into your question on the SOK36 and asked technical staff for advice about the pre-set values on the unit.

Let me know if the below answer is sufficient?

Internal values - <1.80Ω = Green - >1.80Ω = Amber - >90Ω = Red so external nominal values <2.0 ohm and >100 ohm are guaranteed
 
Hang on Phil, am I right in saying these things can't detect Neutral & Earth being swapped?
 
just done a test on the testers,the sock 10 doesnt detect N/E reverse however the sok 36 does,or should I say that it tripped the RCD so that was as far as I got.
 
most of these testers will not see a N-E reversal. your RCD will though as soon as a load is applied to the socket.
 
I've got a Martindale socket tester only use it to quick test and check quickly what sockets are on what circuit. Mines lasted several month no problems. Agree though no substitute for a MFT and full testing. Hope this helps
 