How about this:
Will a RCD work even without a main earth!
We know what it say's, but i'll guarantee you, that virtually every poster that comes on this and other forums, that isn't knowledgeable on TT systems, take that figure in BS 7671 as being the stated maximum and that's what they inevitably will work too!! ...And why i always Poo it off!! lol!!
The whole section on TT earthing needs a thorough sorting out and a bit more guidance wouldn't go amiss either!!
I'm going home (Cyprus) for Xmas this year, and while home, i'll be checking my own TT system. Earlier this year (early summer) it was around 0.93 ohms which has been steadily dropping year on year from around 4'ish ohms.
Here on site, our earth fields were tested middle of last month and recorded 0.17 ohms and 0.21 on the other. The highest value recorded this year was 0.28 and 0.30 respectively, which corresponds to similar test results conducted last year.
It's surprising what can be achieved when you know what you're doing!! lol!!
In a word, no. Fault current needs a path to earth for an RCD to operate. If that path is through you then yeah, it will operate if your bodily resistance combined with the resistance of whatever you happen to be standing on is low enough to allow more than the rated current of the RCD to flow. That said, the requirements of fault protection will not be met if a fault can occur leaving an exposed conductive part live and ready for you to become the earth path!
Im assuming that I'm providing an answer to a genuine and not a rhetorical question![]()
Here on site, our earth fields were tested middle of last month and recorded 0.17 ohms and 0.21 on the other. The highest value recorded this year was 0.28 and 0.30 respectively, which corresponds to similar test results conducted last year!
If you touched a live cable and you was not earthed, you would not get a shock as there is no path to earth. If you make a path to earth then rcd opens simple.
But the whole point is that the system should disconnect before you can touch what is live!
Just to clarify,
the max recommended values I gave earlier were for run of the mill and domestic type circuits and not for the more specialised installations.
Edited last post. Not necessarily!
ADS doesn't rely on the customer being the earth! lol
My question was only 'will it work!' :devilish:
Do not need to discuss all the diferent scenarios.
Then the right answer would be - Not always! lol
Final answer?
What about class 2 lighting circuits that have no earth?
So, is your nightmare an illiterate Electrical Trainee, Part P 'registered' trying to 'do' a TT install
Please give people some credit - the wording is not that technical. There's a big difference between 'over 200 ohms can be unstable' and '200 ohms is the maximum permissible value'?
^ yea!!!!!
I'll leave the nightmares to the clever people like of you...
There are a good few real electricians out there that have never touched a TT system in their lives before, and as has been seen from previous threads and posts, that they will also take that 200 ohm figure as meaning the maximum. Like many other areas in BS 7671 things can be a tad on the ambiguous side, especially if you don't take the time to read things through to fully understand what's being stated.
Does rcd not provide fault protection on said circuit with no cpc. Andy leakage and bang trips.
Domestic wise however, I'd be happy with a couple of 4 footers, an Ra value of 200 ohms and a type-s up front. Last year I happily left a domestic with an Ra value of around 250 ohms even after punching in 8 foot of copper into solid chalk. I went back every month for six months in a row to check its stability and the value hadn't budged.
I dunno Mr D, outside of the realms of our normal installations I could think of a few exotic cases where an RCD could be used that wouldn't use an earth per se
Like what?
Certain IT systems use some pretty exotic protection schemas
also some DC systems are another
I will not mention this part again, let the thread continue un-abated
I like a little banter myself but some of the drivel in this thread boarders on people stuck up their own arses trying to score cheap points. Tone it down guys, its not big and its not clever.
Special thanks to Wirepuller and Engineer 54.
Sorry to be thick, but how does an upstream s,type provide more protection, unless you nail the tails ?There are always going to be situations such as you have described due to horrendous soil/ground conditions, and you're solution of an upfront S type, backing up any standard 30mA RCD's is the route i would also take, in such circumstances...
I too have a good amount of chalky soil on my property in Cyprus, but thankfully not to the extent of causing me major problems on my own system...
I was thinking the same, funny worldInteresting how you give special thanks to the two very people that most on here would regard as being at complete opposite ends of the spectrum with regards to their opinions on domestic TT systems yet refer to others opinions as drivel?
I'll put my tin hat on and take coverSorry to be thick, but how does an upstream s,type provide more protection, unless you nail the tails ?