What was it you said:

"I got a bite! A big one! C'mon lads, get the landing net out ready, this one's gonna be a wriggler!"

Sorry that I'm not interested in winning popularity contests and taking sides in petty arguements.

Neither am I?

I thanked everyone on the thread especially those 'wirepuller' & 'Engineer 54' whose advice I followed and which resolved my situation and in fact got me extra work.

Huh? That's like saying you support Tottenham and Chelsea at the same time? Is it even possible???

However if this leaves you feeling a little under appreciated:

I'm not after your appreciation, nor you patronisation, just the loosening up of your humour belt. We're not here to hate on each other, we're here to offer each other advice and at the same time have a laugh without the fear of having our professional opinions being denounced as drivel. Chill out man!
 
  • Like
Reactions: 2 people
Sorry if I've upset the apple cart gents.

I just find it strange that my singling out of the two individuals whose advice I followed was questioned.

Indeed as my original post clarified "TT virgin" my knowledge on TT is limited and has now been enlightened somewhat.

The end result is I learned and won extra business. Both of which I am thankful for.

It appears that I have affronted one of the inner circle and the wagons are circling so before this gets silly.

Once again thanks for the lessons and the input.

Best regards to you all.
 
Sorry to be thick, but how does an upstream s,type provide more protection, unless you nail the tails ?
Regards

It will provide backup in the unlikely...(although some would argue likely)...event of the 30ma RCD failing to trip on an earth fault.After all on a 'normal' uk TT system with an Ra exceeding that which will operate an OCPD you are completely reliant on a single RCD for earth fault protection.
 
  • Like
Reactions: 1 person
Sorry if I've upset the apple cart gents.

I just find it strange that my singling out of the two individuals whose advice I followed was questioned.




It appears that I have affronted one of the inner circle and the wagons are circling so before this gets silly.

Once again thanks for the lessons and the input.

Best regards to you all.

Not at all, it was referring to other valued posters/posts as "Drivel" which comes across badly
 
I just find it strange that my singling out of the two individuals whose advice I followed was questioned.

It wasn't your singling out of Eng and WP I was questioning, it was the ommission of regognition for the other contributors to the thread and instead, referring to their opinions/advice as drivel .
 
It will provide backup in the unlikely...(although some would argue likely)...event of the 30ma RCD failing to trip on an earth fault.After all on a 'normal' uk TT system with an Ra exceeding that which will operate an OCPD you are completely reliant on a single RCD for earth fault protection.

And it is required when a metal CU/DB is used, it is TD (time delayed) to provide some discrimination to the final circuits 30mA devices so that it doesn't knock the whole lot off in the event of a fault
 
Sorry if I've upset the apple cart gents.

I just find it strange that my singling out of the two individuals whose advice I followed was questioned.

Indeed as my original post clarified "TT virgin" my knowledge on TT is limited and has now been enlightened somewhat.

The end result is I learned and won extra business. Both of which I am thankful for.

It appears that I have affronted one of the inner circle and the wagons are circling so before this gets silly.

Once again thanks for the lessons and the input.

Best regards to you all.

To fill you in a little there have been some pretty hot debates on this historically. I am firmly in the camp of either get a STABLE TN value of Ra that will operate an OCPD...ie sub 1 ohm.....Or dont,in which case it matters not whether it is 20 ohms or 200 ohms as you are totally reliant on an RCD for earth fault protection,and said RCD will trip just the same at 20 ohms or 200 ohms.I'm also of the opinion that where such Ra values are the case the much hyped STABILITY is overated as we know that our 30ma RCD will be good up to 1667 ohms,which means a sub-200 ohms Ra will have to be UNSTABLE to the tune of 1447 ohms before we need to be concerned. Of couse those values would be less if we had a 100ma RCD as well,but you get my drift?
 
  • Like
Reactions: 3 people
"I have returned with this update to thank you all for your input and advice. You have succeeded in enlightening a raw but 2391 trained spark"
 
  • Like
Reactions: 1 person
To fill you in a little there have been some pretty hot debates on this historically. I am firmly in the camp of either get a STABLE TN value of Ra that will operate an OCPD...ie sub 1 ohm.....Or dont,in which case it matters not whether it is 20 ohms or 200 ohms as you are totally reliant on an RCD for earth fault protection,and said RCD will trip just the same at 20 ohms or 200 ohms.I'm also of the opinion that where such Ra values are the case the much hyped STABILITY is overated as we know that our 30ma RCD will be good up to 1667 ohms,which means a sub-200 ohms Ra will have to be UNSTABLE to the tune of 1447 ohms before we need to be concerned. Of couse those values would be less if we had a 100ma RCD as well,but you get my drift?
Don't anyone say I didn't advocate the wearing of a safety helmet. Run for the bunkers the B52's will start bombing soon...
 
  • Like
Reactions: 1 person
images
 
  • Like
Reactions: 4 people
I still say under 200 rock on but the lower the better..
 
Can you get 30mA time delayed RCDs?:devilish:
You can have whatever your heart desires ;)
except anything French, or the Shiant Islands!
 
It basically comes down to, ....those that will make an effort to install a ''Working'' TT system or those that have no intention of making any effort and taking that 200 ohm value as a lame excuse to do virtually nothing, because they are in there mind, complying. Of course stability would then indeed have to be overrated wouldn't it, regardless of what any of the multitude of papers written on the subject have to say!!
 
It basically comes down to, ....those that will make an effort to install a ''Working'' TT system or those that have no intention of making any effort and taking that 200 ohm value as a lame excuse to do virtually nothing, because they are in there mind, complying. Of course stability would then indeed have to be overrated wouldn't it, regardless of what any of the multitude of papers written on the subject have to say!!

In the highly unlikely event that I ever again have to install a TT to either a commercial or large residential then yes...I would be making an effort to get a TN value.I say highly unlikely because these days TNCS is almost always available in my area. I still do a lot of TT's,but small scale. The most recent being a small unit supplying a few sockets for small fairground/entertainment use on a playing field,and temporary civil engineering supplies on a sea front site.For those I believe the standard UK sub 200 ohm and RCD arrangement is perfectly adequate,and if it was 150 ohms at the time of installation and when I came back for a 3 month re-test it had risen to 160 ohms it wouldnt worry me in the least.
That said as Skelton stated in a previous post....I regularly go back to TT's I have installed over the years and cant ever remember initial readings varying to any great degree.
 
In the highly unlikely event that I ever again have to install a TT to either a commercial or large residential then yes...I would be making an effort to get a TN value.I say highly unlikely because these days TNCS is almost always available in my area. I still do a lot of TT's,but small scale. The most recent being a small unit supplying a few sockets for small fairground/entertainment use on a playing field,and temporary civil engineering supplies on a sea front site.For those I believe the standard UK sub 200 ohm and RCD arrangement is perfectly adequate,and if it was 150 ohms at the time of installation and when I came back for a 3 month re-test it had risen to 160 ohms it wouldnt worry me in the least.
That said as Skelton stated in a previous post....I regularly go back to TT's I have installed over the years and cant ever remember initial readings varying to any great degree.

You have often stated in your posts, that soil/ground conditions in you're particular area are not good, and that's fair enough as far as i'm concerned. But you can't go making the same assumptions to those posters that work in and around pretty decent areas, where in some cases i personally know near TN values CAN be attained, in some cases pretty easily too.

Personally i would endeavour to initially treat domestics as i would any other type of installation, only backing off, to let's call it the fall back position, when costs are going to be a major factor.
 
  • Like
Reactions: 1 person
We know what it say's, but i'll guarantee you, that virtually every poster that comes on this and other forums, that isn't knowledgeable on TT systems, take that figure in BS 7671 as being the stated maximum and that's what they inevitably will work too!! ...And why i always Poo it off!! lol!!

The whole section on TT earthing needs a thorough sorting out and a bit more guidance wouldn't go amiss either!!

I'm going home (Cyprus) for Xmas this year, and while home, i'll be checking my own TT system. Earlier this year (early summer) it was around 0.93 ohms which has been steadily dropping year on year from around 4'ish ohms.

Here on site, our earth fields were tested middle of last month and recorded 0.17 ohms and 0.21 on the other. The highest value recorded this year was 0.28 and 0.30 respectively, which corresponds to similar test results conducted last year.

It's surprising what can be achieved when you know what you're doing!! lol!!

So that's what you do with your christmas

think I'll eat turkey and have a good time, knickers to the earth rods
 
I think i can find the time to check my TT system Ra value, it's not as if i'm not home just for the one day like!! I'm sure i'm going to find a lot more maintenance issues that need attending too while home. It's always the same when a house is left unattended for long periods of time!! lol!!

Besides, 15 or so minutes to check the safety of an earthing system, isn't the end of the world, well not mine anyway!!
 
I can just imagine you Eng, the missus inside calling you outside "Sweetheart! The turkey needs carving!", "Just a minute dear, it's of upmost importance that I check the condition of my rod first!", "But you did that yesterday dear, and the day before... And the day before that as well?", "Erm, err, no dear, I don't think I did *chuckle chuckle*, what are you like hey dear? *whilst muttering to yourself>>>* crazy old bat, thinks I'm going senile! Tut".

:D
 
  • Like
Reactions: 2 people
15 mins to check your rods? Why?

I suppose you want your ra values.

You would have checked them before? Why don't you just plug in a metre into a socket and loop it, then do your rcd tests?

2 mins max. Which leaves you 13 mins dig your metre out.
 
Engineer54 a "working" earth what the hell is that? Us electricians call it a stable or un stable earth.
 
Engineer54 a "working" earth what the hell is that? Us electricians call it a stable or un stable earth.
He likes a laugh doesn't he
i think that's the difference between an engineer and a sparky though, we live in the real world.
 
E54 is a qualified part p,pat tester .. Ho ho ho
 
Hi,

How do you PAT test an Earth Rod? Is it done in increments from 0 to 200 ohms?

Regards.
 
Just a visual will do
 
You will all regret your comments when he is here later lol

I think Eng will regret telling us all that the first thing he does on Christmas morning, even prior to opening his stocking from Santa, is to test his earth rod!
 
  • Like
Reactions: 4 people
He must have very long legs.
It's what he gets every year, a bundle of 2.4m rods in his stocking.

And instead of a Christmas card, he gets a brand new Cal Cert for his Earth Tester.
 
  • Like
Reactions: 3 people
I'm waiting for the thunder clap when the time zone in China or Cyprus comes round.....

- - - Updated - - -

Popcorn ready, blanket on knees.

ok go.
 
  • Like
Reactions: 1 person
Nah! E54s bark is worse than his bite lol, he is just a big ol' ----- cat lol

He won't be bothered about us p*** taking about his "rod measuring activities" ooer missus lol , whether over Christmas or not.

If you really want to make him bite, try telling him a 200 ohm rod is just as good as a sub 20 or less ohms one lol, better still a ''twig' is just as good as well
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Max Ze for TT system
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
137

Advert

Thread statistics

Created
MBEINST,
Last reply from
Guest 004,
Replies
137
Views
59,628

Advert