Discuss Max Ze for TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Just to clarify,

the max recommended values I gave earlier were for run of the mill and domestic type circuits and not for the more specialised installations.
 
Just to clarify,

the max recommended values I gave earlier were for run of the mill and domestic type circuits and not for the more specialised installations.

We gathered that :) Any spark worth his weight will know that it isn't always feasible to provide a TT system that delivers TN values to your average domestic installation. It's when you start getting into systems of 200A and over that unless you want to start spending a few thousand on an adjustable 'B' type RCCB, it's best just to provide TN values to protect your metal switchgear.
 
Final answer?
What about class 2 lighting circuits that have no earth?

Yes final answer lol

That is entirely irrelevant. You're relying on a different protective measure entirely, one where RCD's are useless.

Edit: let me rephrase that. The protective measure of using double or reinforced insulation cannot be applied in a domestic setting. Where an existing lighting circuit has no earth and it has not been rewired then you are correct, you are relying on both class 2 fittings and an RCD for addtional protection of the cables buried in walls. This doesn't change my answer though. Bash a nail into that cable and nick the line conductor only, touching that nail doesn't guarantee disconnection :)
 
Last edited:
If you really want to be pedantic Mr E then an RCD just provides differential protection, or an imbalance between the current flow between (for simplicities sake) output terminals and relies on whatever leaves one terminal returning on the other.

In the context of BS7671 (EEBADS/ADS) then this usually utilises the earthing system to work, but it doesn't actually need an earth to work, just merely the conditions to create an imbalance will trip it, look at the way the test button works.
 
So, is your nightmare an illiterate Electrical Trainee, Part P 'registered' trying to 'do' a TT install ;)

Please give people some credit - the wording is not that technical. There's a big difference between 'over 200 ohms can be unstable' and '200 ohms is the maximum permissible value'?

I'll leave the nightmares to the clever people like of you...

There are a good few real electricians out there that have never touched a TT system in their lives before, and as has been seen from previous threads and posts, that they will also take that 200 ohm figure as meaning the maximum. Like many other areas in BS 7671 things can be a tad on the ambiguous side, especially if you don't take the time to read things through to fully understand what's being stated.
 
I'll leave the nightmares to the clever people like of you...

There are a good few real electricians out there that have never touched a TT system in their lives before, and as has been seen from previous threads and posts, that they will also take that 200 ohm figure as meaning the maximum. Like many other areas in BS 7671 things can be a tad on the ambiguous side, especially if you don't take the time to read things through to fully understand what's being stated.

Now that is a statement we can all agree on! lol
 
I dunno Mr D, outside of the realms of our normal installations I could think of a few exotic cases where an RCD could be used that wouldn't use an earth per se, albeit the chances of most of us ever seeing it would be practically nil.

The nearest thing to this is our good old TNC-S system
 
Domestic wise however, I'd be happy with a couple of 4 footers, an Ra value of 200 ohms and a type-s up front. Last year I happily left a domestic with an Ra value of around 250 ohms even after punching in 8 foot of copper into solid chalk. I went back every month for six months in a row to check its stability and the value hadn't budged.





There are always going to be situations such as you have described due to horrendous soil/ground conditions, and you're solution of an upfront S type, backing up any standard 30mA RCD's is the route i would also take, in such circumstances...

I too have a good amount of chalky soil on my property in Cyprus, but thankfully not to the extent of causing me major problems on my own system...
 
Like what?

Certain IT systems use some pretty exotic protection schemas, also some DC systems are another, and I believe someone on here a while back came up with an idea using one (un-conventionally) to protect against a lost Neutral.

But as I said this is way off the beaten track, and is sidetracking this interesting thread, and almost all of us will never ever see it, it was more of an answer to Mr E, and partly the way the test button works (which is why I mentioned TNC-S).
I will not mention this part again, let the thread continue un-abated
 
Certain IT systems use some pretty exotic protection schemas

Every IT system that incorporates an RCD will have an earth sensing device to allow the RCD to operate. Although not an earth per se, it still requires a means to detect an inbalance.

also some DC systems are another

Even a DC RCD needs a means of detecting imbalance between pos and neg which isn't going to happen unless a fault loop has been intentionally made at the supply end. Again, functional imbalance detection would need to be employed.

I will not mention this part again, let the thread continue un-abated

Agreed :)
 
An update on the situation with my TT system.

I today called the DNO 'Electricity North West' and explained that I was at a property to install a couple of extra sockets on the downstairs ring and my Zs readings were unacceptable. I requested that the TT system be changed to TNCS since my subsequent Ze readings mean that no matter what I do to the householders installation I cannot get acceptable Zs readings (OSG Table 2d). I also mentioned that the occupants are in fact living with a dangerous installation since they effectively have little or no fault protection.

The nice man at the other end was quite alarmed and told me that an engineer would be with us before the day is out. Unfortunately this turned into tomorrow morning. However the earthing arrangement will be changed free of charge.

This appears to have bolstered my credibility with the householder and he now wants me to install a fully loaded RCBO unit.

I have returned with this update to thank you all for your input and advice. You have succeeded in enlightening a raw but 2391 trained spark (not sure if that qualifies me as a microwave spark but certainly not a DIYer). I like a little banter myself but some of the drivel in this thread boarders on people stuck up their own arses trying to score cheap points. Tone it down guys, its not big and its not clever.

Special thanks to Wirepuller and Engineer 54.

Everyday is a school day!:)
 
I like a little banter myself but some of the drivel in this thread boarders on people stuck up their own arses trying to score cheap points. Tone it down guys, its not big and its not clever.

I can't see any drivel on here, everyone who has commented has a fair amount of knowledge on TT systems. I can assure you that what you might think is point scoring is purely banter.

Special thanks to Wirepuller and Engineer 54.

Interesting how you give special thanks to the two very people that most on here would regard as being at complete opposite ends of the spectrum with regards to their opinions on domestic TT systems yet refer to others opinions as drivel. I find the term drivel quite disparaging if I'm honest, I can't think of anyone here who hasn't contributed in a positive way to the thread?
 
What was it you said:

"I got a bite! A big one! C'mon lads, get the landing net out ready, this one's gonna be a wriggler!"

Sorry that I'm not interested in winning popularity contests and taking sides in petty arguements.

I thanked everyone on the thread especially those 'wirepuller' & 'Engineer 54' whose advice I followed and which resolved my situation and in fact got me extra work.

However if this leaves you feeling a little under appreciated:

A great big extra special thank you very much to:

D Skelton
:broken_heart: :devilish:
 
There are always going to be situations such as you have described due to horrendous soil/ground conditions, and you're solution of an upfront S type, backing up any standard 30mA RCD's is the route i would also take, in such circumstances...

I too have a good amount of chalky soil on my property in Cyprus, but thankfully not to the extent of causing me major problems on my own system...
Sorry to be thick, but how does an upstream s,type provide more protection, unless you nail the tails ?
Regards
 
Interesting how you give special thanks to the two very people that most on here would regard as being at complete opposite ends of the spectrum with regards to their opinions on domestic TT systems yet refer to others opinions as drivel?
I was thinking the same, funny world
 
No petty arguments on the thread ?????

Most of us on here respect E54 highly, he is entitled to his opinion as much as other highly respected posters are, we were pulling his leg somewhat as we already know what his opinion is lol

That doesn't mean we cannot have our own opinions either, and if you notice we did not say he was wrong, just we all follow the regs which are sometimes badly written and open to interpretation, or sloppily written which implies one thing but could equally mean something else entirely.

Discussions are a good thing, no ?

If you actually understood TT systems a) you would not have posted in the first place, and b) you would see both sides of the debate which was going on in the background, but sadly this appears to have been lost on you.
 
Last edited:
What was it you said:

"I got a bite! A big one! C'mon lads, get the landing net out ready, this one's gonna be a wriggler!"

Sorry that I'm not interested in winning popularity contests and taking sides in petty arguements.

Neither am I?

I thanked everyone on the thread especially those 'wirepuller' & 'Engineer 54' whose advice I followed and which resolved my situation and in fact got me extra work.

Huh? That's like saying you support Tottenham and Chelsea at the same time? Is it even possible???

However if this leaves you feeling a little under appreciated:

I'm not after your appreciation, nor you patronisation, just the loosening up of your humour belt. We're not here to hate on each other, we're here to offer each other advice and at the same time have a laugh without the fear of having our professional opinions being denounced as drivel. Chill out man!
 
Sorry if I've upset the apple cart gents.

I just find it strange that my singling out of the two individuals whose advice I followed was questioned.

Indeed as my original post clarified "TT virgin" my knowledge on TT is limited and has now been enlightened somewhat.

The end result is I learned and won extra business. Both of which I am thankful for.

It appears that I have affronted one of the inner circle and the wagons are circling so before this gets silly.

Once again thanks for the lessons and the input.

Best regards to you all.
 
Sorry to be thick, but how does an upstream s,type provide more protection, unless you nail the tails ?
Regards

It will provide backup in the unlikely...(although some would argue likely)...event of the 30ma RCD failing to trip on an earth fault.After all on a 'normal' uk TT system with an Ra exceeding that which will operate an OCPD you are completely reliant on a single RCD for earth fault protection.
 
Sorry if I've upset the apple cart gents.

I just find it strange that my singling out of the two individuals whose advice I followed was questioned.




It appears that I have affronted one of the inner circle and the wagons are circling so before this gets silly.

Once again thanks for the lessons and the input.

Best regards to you all.

Not at all, it was referring to other valued posters/posts as "Drivel" which comes across badly
 
I just find it strange that my singling out of the two individuals whose advice I followed was questioned.

It wasn't your singling out of Eng and WP I was questioning, it was the ommission of regognition for the other contributors to the thread and instead, referring to their opinions/advice as drivel .
 
It will provide backup in the unlikely...(although some would argue likely)...event of the 30ma RCD failing to trip on an earth fault.After all on a 'normal' uk TT system with an Ra exceeding that which will operate an OCPD you are completely reliant on a single RCD for earth fault protection.

And it is required when a metal CU/DB is used, it is TD (time delayed) to provide some discrimination to the final circuits 30mA devices so that it doesn't knock the whole lot off in the event of a fault
 
Sorry if I've upset the apple cart gents.

I just find it strange that my singling out of the two individuals whose advice I followed was questioned.

Indeed as my original post clarified "TT virgin" my knowledge on TT is limited and has now been enlightened somewhat.

The end result is I learned and won extra business. Both of which I am thankful for.

It appears that I have affronted one of the inner circle and the wagons are circling so before this gets silly.

Once again thanks for the lessons and the input.

Best regards to you all.

To fill you in a little there have been some pretty hot debates on this historically. I am firmly in the camp of either get a STABLE TN value of Ra that will operate an OCPD...ie sub 1 ohm.....Or dont,in which case it matters not whether it is 20 ohms or 200 ohms as you are totally reliant on an RCD for earth fault protection,and said RCD will trip just the same at 20 ohms or 200 ohms.I'm also of the opinion that where such Ra values are the case the much hyped STABILITY is overated as we know that our 30ma RCD will be good up to 1667 ohms,which means a sub-200 ohms Ra will have to be UNSTABLE to the tune of 1447 ohms before we need to be concerned. Of couse those values would be less if we had a 100ma RCD as well,but you get my drift?
 
To fill you in a little there have been some pretty hot debates on this historically. I am firmly in the camp of either get a STABLE TN value of Ra that will operate an OCPD...ie sub 1 ohm.....Or dont,in which case it matters not whether it is 20 ohms or 200 ohms as you are totally reliant on an RCD for earth fault protection,and said RCD will trip just the same at 20 ohms or 200 ohms.I'm also of the opinion that where such Ra values are the case the much hyped STABILITY is overated as we know that our 30ma RCD will be good up to 1667 ohms,which means a sub-200 ohms Ra will have to be UNSTABLE to the tune of 1447 ohms before we need to be concerned. Of couse those values would be less if we had a 100ma RCD as well,but you get my drift?
Don't anyone say I didn't advocate the wearing of a safety helmet. Run for the bunkers the B52's will start bombing soon...
 
images
 

Reply to Max Ze for TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
956
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Quick Question. Despite being 50 I am a newbie electrical installer. Preparing for my retirement from public service. Anyways - my Question. How...
Replies
9
Views
3K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Big argument with a newly qualified electrician with all the necessary qualifications Had to give him a hand later on during the day, nice DB...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock