Discuss Static caravan Ze in the UK Electrical Forum area at ElectriciansForums.net
Status
Not open for further replies.
I've been testing a static caravan installation. At the plastic meter box outside the 'van (which contains an RCD, 16A MCB, meter and 16A socket for the caravan) I get a Ze of 20 ohms and 13.5A PFC. The earth is through the incoming looped SWA of 2 x 2c 16sq.mm cables (crude TNS from the point of view of this caravan but probably TT for the site). The RCD trip times are all fine so all is well.
If I put the earth lead onto the galvanised angle iron which supports the plastic box instead, I get a Ze of 1.16 ohms, 199A PFC!
I'd be more comfortable if the caravan had its own earth rod but I'm not responsible for the system, I'm only here to test the caravan and that is all fine. I'm tempted to bond the angle iron anyway.
If it was up to me every caravan on the site would have its own earth rod.
What does anyone else reckon?
Why bond something outside? It is not possible to create a zone of equal potential
I'm only here to look at the caravan which has the earth imported through the SWA. Yes ideally I would interrogate the site owner and test at the origin. From driving round the site I can see a few (2 or 3 out of a hundred or so) caravans which have what look like 5/8" earth rods beside their meter boxes, the rest just have the looped 2x swa's. So I assume the site is TT but it's really not my remit as I'm only looking at one caravan at the moment.
I assume this is the same thread as this one. This thread closed please keep the same topic to one thread.
Status
Reply to Static caravan Ze in the UK Electrical Forum area at ElectriciansForums.net
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Hi, I've got to a point where I need to complete the EIC for the caravan I've been working on. This isn't a static caravan, so will be going from...
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...